Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
smart ups 5000VA Network Management Card startup
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3012:41 AM. Last Modified: 2024-03-1103:42 AM
smart ups 5000VA Network Management Card startup
Hi,
I am Jamal. We are using APC UPS 5000VA & 3000VA in our environment. Scenario is we have 4x5KVA UPS on which 10xServers are connected for redundancy. we have configured power chute network shutdown to shutdown servers when AC power failure is observed by UPS. Now I have two questions (on lost of AC power to UPS):
1) Is there any way that I put some kind of schedule or bat file in windows that runs PCNS (configured with event) automatically every time when the server is shutdown from windows start menu? Because I want that if we shutdown the servers from windows start menu then there is no need for UPS to stay awake, it should shutdown its outlet group and itself.
2) I want to know the command which PCNS tells UPS that servers are shutting down and you may cut off your output as well with some delay?
In short, We have an application running on 10x servers through which we control the shutdown process of all servers. We just tell one of our server to begin shutting down process on all other servers and shutdown itself on last. I want to put something (which I request from you) in that shutdown process that triggers the PCNS event to tell the UPSs to shutdown automatically because all of servers are shutting down.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3012:41 AM. Last Modified: 2024-03-1103:42 AM
Hi,
If you are going to write a command file that the system will run I suggest disabling Turn UPS off in PCNS. That way only the command file will be telling the UPS to power down.
As for the command file, I recommend you use SNMP. You will find the proper OID by doing a walk of the NMC/s. As an example for my SMX3000RM2U with AP9631 the OID is 1.3.6.1.4.1.318.1.1.1.6.2.1 I recommend turning UPS off gracefully.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3012:41 AM. Last Modified: 2024-03-1103:42 AM
Hi,
If you are going to write a command file that the system will run I suggest disabling Turn UPS off in PCNS. That way only the command file will be telling the UPS to power down.
As for the command file, I recommend you use SNMP. You will find the proper OID by doing a walk of the NMC/s. As an example for my SMX3000RM2U with AP9631 the OID is 1.3.6.1.4.1.318.1.1.1.6.2.1 I recommend turning UPS off gracefully.