smart ups 2200 rm xl

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • smart ups 2200 rm xl
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
3
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

smart ups 2200 rm xl

hi all

i have and old smartups 2200rm xl

model SUA2200RMXLI

i change battery with new one

charged for 100 and do runtime calibration  with 20% load it's just work for 6 min

i remove the load just put one lamp with 50Watte

and gharge the battery with 100% and disconnect the power source

and it's work about 7 min undecided

so i think it's battery problem

change it with worked one and it's the same

this pic from power chute

in pic number 2 some time tell me in ups status avr boost  and some time online >>??

i need it charge battery bigger from it's come with it

4 battery with 7amp i will get 4 battery with 14 or 16 amp for each one

and i found alot youtube talk about mod the code for that problem

the orginal one was 13 and i change it for 2F and many other but the same

so i need the orginal one

and i want frequency to be 60 instead of 50

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

  1. OK, I understand.
  2. The UPS will sync to whatever the input frequency is. So in Egypt, you're input is likely 50Hz, correct? And when you "coldstart" the UPS off of it's battery, the 230V models, default to 50Hz. These models are "auto-sensing" as far as frequency.
  3. Can you be more specific about "it's fail all LED at once" - what does the event log say? Are you indicating all of the LEDs are solid or flash on the front panel, like the UPS is going into a fault condition? We need to know which specific LEDs were on or flashing. For a good calibration result too, I'd suggest at least 20-30% load as well. The lower the load, the less likely a calibration will occur and that it will be super accurate.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

Here are a few pieces of feedback.

  • SUA2200RMXLI is a 230 volt unit. It does 230V in/230V out @ 50 Hz. It may support different output voltages but I don't think you can change the frequency on one of these models.

  • Your UPS reports it is receiving only 200V in, instead of closer to 230V. Thus, it is "boosting" the voltage for you to get it closer to 230V using its internal Automatic Voltage Regulation (AVR) feature. You should look into finding out why you're only receiving 200V. If you already know and it is not going to change, then your UPS is going to be constantly in boost mode which is not what it is designed to do constantly.

  • As far as the calibration, you need to let it charge up to 100% and do a proper calibration. I don't think 20% load is high enough and I'd probably suggest doing a manual runtime calibration if you can, as outlined here (Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US) which recommends at least 30% load for accurate results and it cannot fluctuate more than +/- 5% or else it won't calibrate properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
0
1327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

hi

Angela N. thanks for your reply ..

1- the boosting is not all time some time it in online mode .. i think it's weak of voltage ( EGYPT)

i could attach voltage stablizer for fix this problem

but the main problem is it's not fully charge the battery .. after 2 midnighte the voltage will be  220 stable until 11am so it's good time to fully charge without boosting mode

2-http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA2200RMXLI3U

its show frequency from 47 to 60 So it's must be have

3- i wait for 100 charge and do calibration it's fail all led at once and refuse to do calibration

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
0
1328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

  1. OK, I understand.
  2. The UPS will sync to whatever the input frequency is. So in Egypt, you're input is likely 50Hz, correct? And when you "coldstart" the UPS off of it's battery, the 230V models, default to 50Hz. These models are "auto-sensing" as far as frequency.
  3. Can you be more specific about "it's fail all LED at once" - what does the event log say? Are you indicating all of the LEDs are solid or flash on the front panel, like the UPS is going into a fault condition? We need to know which specific LEDs were on or flashing. For a good calibration result too, I'd suggest at least 20-30% load as well. The lower the load, the less likely a calibration will occur and that it will be super accurate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of