The battery is not installed properly

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • The battery is not installed properly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:18 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
2
2515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:18 AM . Last Modified: ‎2024-03-12 03:08 AM

The battery is not installed properly

Why two "not installed"  "already installed" alarms occur frequently.      The UPS is Smart-UPS 3000 RM with AP9630 card.     It sounds the battery is new and from APC.       The product detail as below:

apc>about

E000: Success

Hardware Factory

---------------

Model Number:           AP9630

Serial Number:          ZA1241005544

Hardware Revision:      05

Manufacture Date:       10/04/2012

MAC Address:            00 C0 B7 98 A4 46

Management Uptime:      78 Days 17 Hours 59 Minutes

Application Module

---------------

Name:                   sumx

Version:                v5.1.7

Date:                   Dec  1 2011

Time:                   13:01:45

APC OS(AOS)

---------------

Name:                   aos

Version:                v5.1.7

Date:                   Nov 22 2011

Time:                   09:53:57

APC Boot Monitor

---------------

Name:                   bootmon

Version:                v1.0.2

Date:                   Jan 21 2010

Time:                   13:35:57

E000: Success

Status of UPS: On Line, Bad Battery, No Other Alarms Present

Last Transfer: Due to software command or UPS's test control

Runtime Remaining: 8 hr 30 min

Battery State Of Charge: 100.0 %

Output Voltage: 117.3 VAC

Output Frequency: 60.0 Hz

Output Watts Percent: 11.7 %

Output VA Percent: 11.7 %

Output Current: 3.00 A

Input Voltage: 117.3 VAC      --->I did check few times within 1 hour , sounds the input voltage is stable

Battery Voltage: 54.5 VDC

Internal Temperature: 36.9 C, 98.4 F

Self-Test Result: Not Available

Self-Test Date: 05/23/2014

Calibration Result: Not Available

Calibration Date: Unknown

Attachments
config.ini.zip
data.txt.zip
event.txt.zip
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
0
2506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

When you see this type of thing, it is likely the battery, or very rarely, the UPS and it's ability to detect that the battery is present. If a self test is not completing, it sounds like there is a problem with this battery and it's capability to support the load properly. I see a couple of instances in data.txt, where the battery voltage has dropped way down.

Anyway, if this is a genuine APC replacement battery, you'll need the serial number on that replacement battery and depending on what that is, a proof of purchase possibly, and then you'll want to pursue a replacement with tech support in my opinion. Something isn't right with it. If a new battery does not solve the issue (which I think is unlikely), then it may be a problem with the UPS. I doubt this because of the voltage drops in data.txt - they seemed to indicate an issue with the battery to me.

If it turns out it is not a genuine APC replacement battery, then you'd want to pursue a replacement with wherever it was purchased.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
0
2506
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

I tried to do self-test ,   it sounds all attached devices are rebooted , but the UPS doesn't reboot. 

apc>ups -st

E000: Success

State: On Line, Bad Battery, No Other Alarms Present

apc>about

E000: Success

Hardware Factory

---------------

Model Number:           AP9630

Serial Number:          ZA1241005544

Hardware Revision:      05

Manufacture Date:       10/04/2012

MAC Address:            00 C0 B7 98 A4 46

Management Uptime:      78 Days 18 Hours 26 Minute

apc>detstatus -all

E000: Success

Status of UPS: On Line, Bad Battery, No batteries installed, No Other Alarms Present

Last Transfer: Due to software command or UPS's test control

Runtime Remaining: 8 hr 30 min

Battery State Of Charge: 100.0 %

Output Voltage: 118.0 VAC

Output Frequency: 60.0 Hz

Output Watts Percent: 11.7 %

Output VA Percent: 11.7 %

Output Current: 3.00 A

Input Voltage: 118.0 VAC

Battery Voltage: 54.5 VDC

Internal Temperature: 36.9 C, 98.4 F

Self-Test Result: Invalid

Self-Test Date: 05/23/2014

Calibration Result: Not Available

Calibration Date: Unknown

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

0 Likes
0
2507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:19 AM . Last Modified: ‎2024-03-12 03:08 AM

When you see this type of thing, it is likely the battery, or very rarely, the UPS and it's ability to detect that the battery is present. If a self test is not completing, it sounds like there is a problem with this battery and it's capability to support the load properly. I see a couple of instances in data.txt, where the battery voltage has dropped way down.

Anyway, if this is a genuine APC replacement battery, you'll need the serial number on that replacement battery and depending on what that is, a proof of purchase possibly, and then you'll want to pursue a replacement with tech support in my opinion. Something isn't right with it. If a new battery does not solve the issue (which I think is unlikely), then it may be a problem with the UPS. I doubt this because of the voltage drops in data.txt - they seemed to indicate an issue with the battery to me.

If it turns out it is not a genuine APC replacement battery, then you'd want to pursue a replacement with wherever it was purchased.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of