scheduled shutdown during power outage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • scheduled shutdown during power outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

0 Likes
2
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

scheduled shutdown during power outage

so, I have several smart-ups 2000s (smx2000rmlv2u) with nmc2s running 5.1.7 firmware that I used to shutdown the upses during a power outage with a power back on setting of 5 hours later (scheduled shutdown). shutdown occured as expected, but, 5 hours later, the upses didn't seem to come back online. A/C power still off, so I'm wondering if that is why, even though the units were shut down while they still had plenty of runtime left (60+ minutes on the most drained unit) that the units have come back. the only loads on the units are the network switches to which the nmc2s are connected, so, no power, no network with which to remotely tell what's happening. since it's a (sort of) remote location, my main concern is that the units came back, but for some reason, the switched outlet groups stayed off, potencially exposing the upses to bad power by being on (hate to see my upses get killed by this). the other question is, if it is due to lack of A/C power is why the units are still off, will the units come back to life without manual intervention once power is restored?

thanks for any answers I can get!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 5.1.7
  • nmc2
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

Hi,

The UPS are designed to restore power to the outlets once AC is restored so the UPS are working as designed.

On 5/13/2015 7:07 PM, Verta said:

my main concern is that the units came back, but for some reason, the switched outlet groups stayed off, potencially exposing the upses to bad power by being on (hate to see my upses get killed by this).

Again, if there is no AC available the UPS outlets stay off so there is no danger to the attached load and if there is no AC then there is no danger to the UPS. There is always the possibility when AC is restored that there could be a surge that could damage the UPS but they are designed to deal the typical power up surge/spike.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

0 Likes
0
1262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

Hi,

The UPS are designed to restore power to the outlets once AC is restored so the UPS are working as designed.

On 5/13/2015 7:07 PM, Verta said:

my main concern is that the units came back, but for some reason, the switched outlet groups stayed off, potencially exposing the upses to bad power by being on (hate to see my upses get killed by this).

Again, if there is no AC available the UPS outlets stay off so there is no danger to the attached load and if there is no AC then there is no danger to the UPS. There is always the possibility when AC is restored that there could be a surge that could damage the UPS but they are designed to deal the typical power up surge/spike.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

0 Likes
0
1261
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:40 PM . Last Modified: ‎2024-03-01 12:30 AM

thanks; the units did return to normal operation without manual intervention once power was restored. guess I just found it odd initially when the units ignored the "power back on" part of the scheduled shutdown while A/C power was still unavailable even though I knew they had plenty of runtime left. thinking through how the units act when first installed regarding not turning on initially if there isn't input power made the situation seem less odd and more to be expected, but, of course, hindsight is 20/20!

thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore