hi, i have apc BE600M1 replace new battery still not working and keep beeping i check the output not ac voltage
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:17 PM . Last Modified: 2024-03-19 03:15 AM
Hi,
Have you reset the UPS?
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
If that does not resolve the issue you should contact local support. IF the unit is under warranty they will assist with a replacement.
Local support contact information will be found at this link.
https://www.apc.com/us/en/support/contact-us/index.jsp
You may need to change the region in the upper left of the contact us web page.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 11:17 PM . Last Modified: 2024-03-19 03:15 AM
Hi,
Have you reset the UPS?
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
If that does not resolve the issue you should contact local support. IF the unit is under warranty they will assist with a replacement.
Local support contact information will be found at this link.
https://www.apc.com/us/en/support/contact-us/index.jsp
You may need to change the region in the upper left of the contact us web page.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.