Our Symmetra 20K shows a few messages in the event log like this :
11/17/2010 23:04:41 UPS: A power module fault no longer exists.
11/17/2010 23:04:21 UPS: A power module fault exists.
11/17/2010 11:05:58 UPS: A power module fault no longer exists.
11/17/2010 11:05:38 UPS: A power module fault exists.
Its happened before and I dismissed it as a fluke since it cleared 20 seconds later.
Since it now happened again does anyone know if were in trouble ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:05 AM . Last Modified: 2024-03-19 01:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:05 AM . Last Modified: 2024-03-19 01:10 AM
We saw the same thing with our Symmetra 20K.
We pulled out the faulty module and pulled an extra from our inactive Symmetra 20k and seated it.
The strange thing is when we did that Power Module 1 came back online as well as the power module (# 2) we replaced with the spare.
As of now we have all 3 power modules showing as installed and online.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:05 AM . Last Modified: 2024-03-19 01:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:05 AM . Last Modified: 2024-03-19 01:10 AM
Try to upgrade your network management card firmware.
link to apc site and choose your network management card model and download the firmware.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:05 AM . Last Modified: 2024-03-19 01:10 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:05 AM . Last Modified: 2024-03-19 01:10 AM
We saw the same thing with our Symmetra 20K.
We pulled out the faulty module and pulled an extra from our inactive Symmetra 20k and seated it.
The strange thing is when we did that Power Module 1 came back online as well as the power module (# 2) we replaced with the spare.
As of now we have all 3 power modules showing as installed and online.
Link copied. Please paste this link to share this article on your social media post.