"Communication Lost" Smart UPS 1000 W2K3 R2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "Communication Lost" Smart UPS 1000 W2K3 R2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:32 AM

0 Likes
5
919
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:32 AM

"Communication Lost" Smart UPS 1000 W2K3 R2

Hi all,

We have a large number of W2K3 R2 servers at remote sites hooked up to Smart UPS 1000s by USB. They seem to have a tendency to lose communication for no apparent reason and not regain it.
The driver is still present, and reinstalling it succeeds with no effect. Restarting the agent service has no effect. I neglect to mention the server or console as the web interface provided by the agent also reports comms lost.

I should mention we are having exactly the same problem with an SUA3000RM on another W2K3 server too.

Any thoughts? Obviously this is a big issue as we cannot easily gain physical access to the equipment.

Running 7.0.5.

Cheers
Rob

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

0 Likes
0
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

I apologize if that previous post came off as touchy.

I understand that it's a critical setup, as is the case we run into all the time doing support. There usually is a requirement of some type of downtime window that most customers receive to do troubleshooting.

The only reason I threw it out there is because it seems to be a universal problem, and is more than just a coincidence that it's occurring on two different systems that both have the ability to have either one or the other means of communication.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

0 Likes
0
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

Two different models of UPS, but about 5 or 6 different physical units exhibiting the same issue.

I apologise for my disobedience, but these UPS' are all running critical systems, and are also several miles away.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

0 Likes
0
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

Rob,

Have you tried to brain-dead the UPS and fully enable the USB support on the UPS?

To do so:

Power off the load attached to the UPS
Power off the UPS and disconnect from the wall
Remove any communications cables
Depress the Off button for 4-6 seconds until you hear a click.

Load everything back up and keep an eye on it.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

0 Likes
0
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

I haven't, however as I mentioned this applies to multiple different units, and I don't therefore see that it could be a one-off fault fixed by what is effectively rebooting the unit.

Worthy of note that if I wanted to re-establish USB comms I could disconnect the USB cable and reconnect it. However this will not fix the re-occurring issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

0 Likes
0
917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

You have two different UPS's both of which have serial and USB support. I would try that first.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

0 Likes
0
918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:27 AM . Last Modified: ‎2024-03-08 02:31 AM

I apologize if that previous post came off as touchy.

I understand that it's a critical setup, as is the case we run into all the time doing support. There usually is a requirement of some type of downtime window that most customers receive to do troubleshooting.

The only reason I threw it out there is because it seems to be a universal problem, and is more than just a coincidence that it's occurring on two different systems that both have the ability to have either one or the other means of communication.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore