"Button Error" Smart UPS SRT 5000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "Button Error" Smart UPS SRT 5000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:12 PM

0 Likes
7
15976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:12 PM

"Button Error" Smart UPS SRT 5000

Hello All,

I have a "Button Error" on the LCD screen which is on an orange background and is interfering with the outputs to the rear of the UPS.

There doesn't seem to be a lot about this anywhere online, on here or in the manual.

Mr problems are:

1. Access via Web Page to UPS on internal IP address showing following error on the web page "The Application Is Incompatible With This APC OS
You are attempting to access an APC device.  
The application you are trying to load is incompatible with the current APC OS. Please verify the correct firmware is loaded.

I have upgraded the firmware to version 04.1 using the correct APC application via USB which is the latest version - still a problem.

2. On the LCD of the UPS Controller itself "Button Error" and orange screen. When on 02.6 firmware outputs switched off. upgraded firmware to 02.9 then 04.1. Outputs now back on. When going to 04.1 the LCD went back to normal grey / blue for about 30 seconds but then back to orange "Button Error" with error bleep every second.

I am not sure where to go next to clear this error. Does "button error" refer to a physical button problem? having updated firmware i was hoping that the error would clear or at least i could access UPS controller over the WEB on its internal ip address to try to clear the errors. The electrical outputs of the UPS are up and down at the moment.

 

any help would be great. I havent tried a cold reboot as yet but i dont think this will help.

 

thanks
 
 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • button
  • error
  • orange
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

Hi Christian,

I apologize for the late reply. I would like to ask for the exact model and serial number of the UPS that has the "button error". I have experienced a similar problem a few months back and we replaced the UPS.

From how you described it, I think we have done most troubleshooting, but for most of the SRT errors, if the cold boot (coldstart) or a restart has not cleared the problem, we need to have it replaced.

I hope this helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

1 Like
0
15972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

Hello - 

The "Button Error" is a physical issue with the button on the LCD display of the UPS. In some earlier firmware revisions you may see an unexpected behavior where this will cause the UPS to turn off the output power. If you are running the latest firmware (which is likely 4.1) the UPS will just report the error and it will not affect the output power of the UPS. If your UPS is reporting this error and is under warranty, you should contact your local tech support team for further assistance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

Hi.

I had same situation yesterday. At night my Smart UPS STR 8000 turned off all outlet groups and showed "Button Error" warning message on the LCD display.  I made power-on, but the warning message is still present. Later I had many troubles with our equipment and with my boss. 

Firmware Revision:

UPS 04.4 (ID1014)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:21 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:21 PM . Last Modified: ‎2024-03-06 11:11 PM

Hi Dave - 

I apologize - This is clearly not a good experience to have with a new unit. Unfortunately this is a physical issue with the LCD display itself. I would suggest you contact tech support for assistance with getting a warranty replacement.

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

Hi Christian,

I apologize for the late reply. I would like to ask for the exact model and serial number of the UPS that has the "button error". I have experienced a similar problem a few months back and we replaced the UPS.

From how you described it, I think we have done most troubleshooting, but for most of the SRT errors, if the cold boot (coldstart) or a restart has not cleared the problem, we need to have it replaced.

I hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

I can't help with the "Button Error" but problem (1) with the Network Management Card should be easy to fix. Grab the latest firmware here:

http://www.apc.com/us/en/tools/download/

UPS Network Management Card should be near the end of the dropdown list. You're looking for (at the time of writing) SUMX 640. Update your card to that. It should hopefully resolve the "Application Incompatible" message.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

Dear Sir,

          I am also facing almost same issue in my UPS. The Fault shown in Event logs is "local display button fault" exist. Due to which my outlet groups turned off. As i am an engineer and i have to explain my boss the root cause of shutdown of load which i cant find other then the issue "local display button fault". Kindly tell me some solid reason about this fault.

Thanks & Regards

Raja Haroon Rasheed

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

1 Like
0
15973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

Hello - 

The "Button Error" is a physical issue with the button on the LCD display of the UPS. In some earlier firmware revisions you may see an unexpected behavior where this will cause the UPS to turn off the output power. If you are running the latest firmware (which is likely 4.1) the UPS will just report the error and it will not affect the output power of the UPS. If your UPS is reporting this error and is under warranty, you should contact your local tech support team for further assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:20 PM . Last Modified: ‎2024-03-06 11:11 PM

Hi.

I had same situation yesterday. At night my Smart UPS STR 8000 turned off all outlet groups and showed "Button Error" warning message on the LCD display.  I made power-on, but the warning message is still present. Later I had many troubles with our equipment and with my boss. 

Firmware Revision:

UPS 04.4 (ID1014)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:21 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:21 PM . Last Modified: ‎2024-03-06 11:11 PM

I have an SRT-6000VA unit, has been installed for less than a month. Yesterday afternoon the UPS powered off the controlled outlets with "Button Error" on the display. Fortunately I was able to power it back on and then proceeded to restore our IT infrastructure back to normal operation. The display is still showing "Button Error".

The firmware rev is ID1013UPS 04.7

Why is this known fault still occurring on new equipment? I purchased APC as it is "the" name in UPS hardware but was hesitant to use a UPS that had controlled outlets for this very reason, I should have gone with my gut instinct.

This is very poor quality control.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:21 PM . Last Modified: ‎2024-03-06 11:11 PM

0 Likes
0
15974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:21 PM . Last Modified: ‎2024-03-06 11:11 PM

Hi Dave - 

I apologize - This is clearly not a good experience to have with a new unit. Unfortunately this is a physical issue with the LCD display itself. I would suggest you contact tech support for assistance with getting a warranty replacement.

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore