Hi.
I have an AP9225 master switch and am thinking about buying an AP9225EXP. I am a bit of a noob in this area so please bear with me. The existing set up is using 2 3000 XL units which power 6 servers - 4 of the servers are 1U, 1 is 3U and 1 is 5U. Additionally there is 1 PC and and 1 IBM EXP400 array which is only using 4 discs on side. The load is spread across both UPS units but I don't like how it was done - set up before my joining the company.
The servers have redundant power supplies and I have noticed the monitoring cables are attached to some of the servers. It seems this set up was started but not completed. So I am hoping someone may help me to understand what ways are possible to properly set this up...
For example:
Should each server's PSU's be plugged into different UPS units?
How can I calculate the load that all servers produce?
Will an expansion unit (AP9225EXP) help me to effectively manage the start up/shutdown sequence if power goes out completely?
What can I read to gain more of an understanding?
Thanks for any and all suggestions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:24 AM
yes i'd recommend upgrading.
[take a look at this link here for doing that|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=768]
each UPS needs to have a network management card inside of it. you cant daisy chain them together.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:25 AM
Hi and thanks for the reply.
You know it's funny - the outsourced IT services company had already sold the company I work for a management card plus a master switch a few years back.
So now just to be certain I understand you, we could avoid using the master switch and buying the exp unit IF we were to use the management card plus install the powerchute software on all servers? The serial cables of course would still be required as well - is that correct? That would be a heck of a lot simpler...
I am still trying to figure out the SNMP part for the external array - an IBM EXP400. It's got to be powered on before the server it's attached to starts up otherwise the array won't be seen properly.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:25 AM
if you use a network management card inside the UPS, you do not need any type of serial connection to the servers. the only time you'd need to use a serial cable is to configure network management card locally to put the IP address on it. communication and shutdown will be done over the network only.
you'd install the network management card into the UPS, configure it with an IP address, install powerchute network shutdown on each computer you have plugged into the UPS for power and want to shutdown gracefully when the UPS turns off due to low battery or some type of power event (which the settings are very customizable).
you can stagger shutdowns, run command files, etc and things like that if you need to and that software is free.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:25 AM
Hi again.
My management card details are as follows:
model - AP9617
hardware revision - A10
AOS version - 1.1.6
So I am thinking I should be able to manage all the servers from this one card and remove the master switch. Should I upgrade the card's firmware or should I look at getting a newer card? I just re-read this and was thinking maybe I need a 2nd switch for my other UPS or can I chain the 2 UPS units together?
Thanks very much in advance.
Message was edited by: james.bowes
Message was edited by: james.bowes
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-28 04:34 AM . Last Modified: β2024-03-18 04:24 AM
yes i'd recommend upgrading.
[take a look at this link here for doing that|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=768]
each UPS needs to have a network management card inside of it. you cant daisy chain them together.