Posted: 2021-06-28 04:33 AM . Last Modified: 2024-03-18 04:25 AM
I am a little stumped on this one. The UPS keeps doing 2 self tests a day apart instead of one.
I have a NMC2 installed (9631) with the 6.40 software.
I set it for 7 or 14 days and when it is due for a test it will complete one, then do another the next day.
Since I spotted this I disabled self test on the card and checked the UPS config via the panel and it was also disabled. Set it for a 14 day test and left it alone thinking it was sorted.
Saturday and today it did a self test and I have no idea why it does the 2nd?
From the logs
18.04.2016 10:30:14 Device UPS: RFC1628 MIB UPS test completed. 0x3603
18.04.2016 10:30:14 Device UPS: Self-Test passed. 0x0105
18.04.2016 10:30:06 Device UPS: Self-Test started by automatic timer. 0x0137
17.04.2016 08:36:51 System Web user 'apc' logged out from 192.168.1.10. 0x001F
17.04.2016 07:36:39 apc Web user 'apc' logged in from 192.168.1.10. 0x0015
16.04.2016 23:20:13 Device UPS: RFC1628 MIB UPS test completed. 0x3603
16.04.2016 23:20:13 Device UPS: Self-Test passed. 0x0105
16.04.2016 23:20:03 Device UPS: Self-Test started by automatic timer. 0x0137
Any ideas?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
That's what I recall with mine. If no tests are configured, you should still get one on a periodic basis to verify the battery is good to go when needed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
Hi,
What is the exact model and serial number of the Smart-UPS. You will find the information on the bar code sticker on the back the unit.

If the model is SMT2200 or SMX2200 what firmware version is the UPS running? You will find the UPS firmware information and the model and serial number in the NMC under About - UPS or from the LCD panel under the About menu.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
On 4/18/2016 9:58 AM, Bill said:Hi,
What is the exact model and serial number of the Smart-UPS. You will find the information on the bar code sticker on the back the unit.
If the model is SMT2200 or SMX2200 what firmware version is the UPS running? You will find the UPS firmware information and the model and serial number in the NMC under About - UPS or from the LCD panel under the About menu.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
Hi,
The self-test parameters are stored on the UPS so the issue is with the SMT2200.
The firmware is up-to-date so you could reset the unit
1) Turn off and unplug UPS from wall
2) Disconnect Battery
3) You may hear an audible "click" from the UPS.
4) Reconnect battery, plug unit back in the wall, and turn UPS back on
If that does not resolve the issue and the unit is under warranty you could request a replacement.
You could ignore the issue since it is cosmetic and running a self-test a day apart will not hurt the unit.
Another option is to set the UPS to not run an automatic self-test and run the test manually every 2 weeks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
I have set it to "UPS Startup and every 7 Days since last test" and will see what happens in a week, if it does it again I will brain dead the unit and try it again.
Thanks Bill.
Gareth.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
I owned an SMT3000 that was on the 7.1 firmware that was doing the same thing. This was the hardware revision level that could not be updated to the version 8.x firmware. There is a known hardware issue with earlier revision units that will, indeed, execute a self-test even when one is not configured or, in your case, two if you configure one test.
Being OCD, I replaced my unit, but if I were to do it all over again, I wouldn't care.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
Thanks Joe, I have now set it to do one at startup as it still did 2. I assume it will throw in a regular extra one for the fun of it. I can live with this if it does as I expect.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:34 AM . Last Modified: 2024-03-18 04:25 AM
That's what I recall with mine. If no tests are configured, you should still get one on a periodic basis to verify the battery is good to go when needed.
Link copied. Please paste this link to share this article on your social media post.