Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

peak versus Avg

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • peak versus Avg
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

0 Likes
3
799
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

peak versus Avg

In a data center with dual UPS systems of 100KVA, each UPS shows about 25% peak , avg 16% load on the panel. Do I use the peak or the Avg to determine available capacity? I can't go over 50% right? So do I have 25% capacity left or 34%?
Thanks

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

0 Likes
0
801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

Code typically specifies the 80% rule for things like breakers so that you would only run a 20A breaker at 16A max. However UPS are designed to run at their rated 100% limit indefinitely. So if you two 100KVA UPS you can run each up to 50KVA if you plan on having your load fail over to the other UPS during a failure. If that was to occur and you had exactly 50KVA on each then the online UPS would assume the other 50KVA and run at 100kva 100% load as long as you needed to. The only issue you run into with fully loading a unit is that loads often fluctuate and can cause an overload condition which is why some data center managers choose to stay below their max by an order of 10 or 20%. In your case since you have 100KVA units I'd run them up to 45% and in a fail over the online UPS would still be loaded at 90% and would give you 10% of extra capacity if needed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

0 Likes
0
801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

To clarify he cannot go over 50% of BOTH units capacity. IOW, he can load up tp 100kva total. Persoanlly I would stay below 80%.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

0 Likes
0
801
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

Thanks for the responses!

I was plannning on keeping each UPS below 40% so in a failover one UPS would stay below 80%. Is that a code requirement or just a best practice?
Code does require all circuits to stay below 80%, right?

Thanks Again!

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

0 Likes
0
802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:03 AM . Last Modified: ‎2024-03-19 01:12 AM

Code typically specifies the 80% rule for things like breakers so that you would only run a 20A breaker at 16A max. However UPS are designed to run at their rated 100% limit indefinitely. So if you two 100KVA UPS you can run each up to 50KVA if you plan on having your load fail over to the other UPS during a failure. If that was to occur and you had exactly 50KVA on each then the online UPS would assume the other 50KVA and run at 100kva 100% load as long as you needed to. The only issue you run into with fully loading a unit is that loads often fluctuate and can cause an overload condition which is why some data center managers choose to stay below their max by an order of 10 or 20%. In your case since you have 100KVA units I'd run them up to 45% and in a fail over the online UPS would still be loaded at 90% and would give you 10% of extra capacity if needed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of