Hello,
With PowerChute network Shutown, it's possible to defined a order for shutdown a agent ?
Philippe.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:09 AM . Last Modified: 2024-03-18 02:41 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:09 AM . Last Modified: 2024-03-18 02:41 AM
Hi,
If you are looking for a sequenced server shut you have the option of setting each agents on battery delay to different times. An example is have one agent start the OS shutdown after the UPS has been on battery for 5 minutes and another start the shutdown after the UPS has been on battery for 10 minutes. Another option is to configure Runtime Remaining below Threshold. See page 34 of the User's Guide for more information is runtime remaining below threshold.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:09 AM . Last Modified: 2024-03-18 02:41 AM
Ok,
Thanks.
Philippe