Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

one Back-UPS 500 offers minimal data, the other has access to full menu

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • one Back-UPS 500 offers minimal data, the other has access to full menu
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:38 AM

0 Likes
13
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:38 AM

one Back-UPS 500 offers minimal data, the other has access to full menu

This was originally posted on APC forums on 10/20/2012


Hello, I'm using two Back-UPS 500and I've runned into this weird problem: one of them offers access to all kind of options (voltage and so on) while the other basically offers nothing that isn't into the built in windows UPS management. I've tried using several versions of the PowerChute personal but it's the same in all of them. I've installed the APC software quite recently, because of the fact that the power grid started to have undervoltage at peak hours and the two UPS were kicking in too often. On one I've been able to adjust the voltage and solve the problem but in the other one the menu is not even present. You can see in the attachment what I get in PowerChute on this UPS.
What should I do to get access to the full menu? Maybe a fw upgrade?

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 500
  • back-ups
  • disabled
  • menus
  • PowerChute
  • problem
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This reply was originally posted by Angela on APC forums on 11/19/2012


all of the LEDs will flash briefly and then you push the power button while in this mode and when you keep pushing it, the LEDs will change indicating high (3 LEDs flashing), medium (only 2 LEDs flashing) and then low (1 LED flashing). if you keep pushing, it will toggle between all of the modes.

See Answer In Context

Reply
Share
Replies 13
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:38 AM

0 Likes
0
1305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:38 AM

This was originally posted on APC forums on 10/20/2012


And here you have the technical data for the Back-UPS 500 that has all the options enabled. The firmware appears to be much more recent. Do you have this fw awailable for download, so I can get full functionality on the first unit?

Attachments
Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:38 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:38 AM

This reply was originally posted by Angela on APC forums on 10/22/2012


i believe you have two types of UPS here. one reports as a Back UPS and the other one shows as Back UPS CS which is a different product line. i'd imagine that the older UPS does not support reporting as much data as the newer one does.

these types of units are not firmware upgradable unfortunately.

Reply
Share
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This was originally posted on APC forums on 10/22/2012


I'm afraid this isn't the case. Both units are clearly labeled "Back-UPS CS" on the front.I can add pics if needed. Also both units are of the same type, BK500EI. Also reporting more or less parameters is one thing and not being able to adjust the voltages is quite another. ( the fact that one firmware reports to the PowerChute that the unit is "Back-UPS" and the other reports "Back-UPS CS" shouldn't take precedence over what's written on the front side of the UPS... )

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This reply was originally posted by Angela on APC forums on 10/23/2012


ok, i was on the right track. these units have changed internally several times and unfortunately, they keep the SKU the same so in your situation i believe you have essentially two different firmwares/units they just happen to have the same SKU.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This reply was originally posted by Angela on APC forums on 10/23/2012


let me double check on that. my thought is we kept the same SKU/model number but the firmware or internal hardware platform was changed but that is just an educated guess. i'll see what i can find out to explain this.

Reply
Share
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This was originally posted on APC forums on 10/23/2012


Thank you, looking forward to your reply. The main interest point for me is the capability to change the voltages.

Reply
Share
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This was originally posted on APC forums on 10/23/2012


And there's no way I can get voltage settings (and self test) on the first unit? That seems really odd, to say the least...

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This reply was originally posted by Angela on APC forums on 10/23/2012


i agree - some of the features may be missing but it is normal for this product line to keep same SKU but change firmware features, etc

i do believe you should see the voltage threshold options on each for a UPS of this type. i am not quite sure what the root cause of it is but my gut feeling is the firmware difference. it does not make sense to me that if it was supported, you'd be able to see the runtime and online or on battery status but the rest is missing. to me that just means it does not support it for one reason or another (as silly as that sounds).

on these models, i believe you may be able to change sensitivity and/or voltage settings via the front switch if you leave the UPS plugged into AC power but turn it off and hold down the on/off button for about 10 seconds. some lights will flash and you can adjust the sensitivity that way.

that is the best advice I can give at this point. you could try braindeading and rebooting the UPS just to see but i feel like it won't help. worth a try though. to braindead this one, remove and turn off the attached load and data cable, turn off the UPS and remove it from AC power. then disconnect the battery connection and hold down the off button for 5-10 seconds. then reconnect everything and see what you get.

Reply
Share
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This was originally posted on APC forums on 11/18/2012


Thank you. Can you elaborate a bit about the specific procedure? How do you know when you are increasing/decreasing the voltage and the sensitivity?

Message was edited by: AdrianA

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This reply was originally posted by Angela on APC forums on 11/19/2012


all of the LEDs will flash briefly and then you push the power button while in this mode and when you keep pushing it, the LEDs will change indicating high (3 LEDs flashing), medium (only 2 LEDs flashing) and then low (1 LED flashing). if you keep pushing, it will toggle between all of the modes.

Reply
Share
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This was originally posted on APC forums on 11/20/2012


What do you know, it worked. 🙂 Actually there will be first silence/nothing happens for about 7 seconds, then a loud beep then another few seconds of ... nothing, then the LED's start flashing. Only at this point you take your finger off the button and start pressing it in order to adjust.
Now the UPS won't kick in at 180V, probably the min voltage is lower. 🙂
And the final question: do you know where I can download a datasheet/manual for this model, so I can figure out the exact parameters for the 3 settings available (high, med and low most likelly)?
thanks a lot.

Message was edited by: AdrianA

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This reply was originally posted by Angela on APC forums on 11/26/2012


check here: http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BK500EI&tab=documentation -> http://www.apcmedia.com/salestools/ASTE-6Z7VBG_R0_EN.pdf

let me know if you need anything else.

Reply
Share
AdrianA_apc
Crewman AdrianA_apc
Crewman

Posted: ‎2021-07-01 01:39 AM

0 Likes
0
1306
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:39 AM

This was originally posted on APC forums on 11/30/2012


Unless someone figures out a way to flash this old UPS with a more recent firmware, that would be it 🙂 . Thanks a lot.

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc