load factor vs battery life

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • load factor vs battery life
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
127
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

0 Likes
3
1034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

load factor vs battery life

Hello,

We use Smart UPS 750 units and experience 10 - 14 month battery life.  I assume this relates to our high load: 3.2 Amps at 220V. Is there a chart or documentation available documenting load vs battery-life-expectancy?

My thanks in advance,

Bruce

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

0 Likes
0
1034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

BTW, these APC "smart" UPSs are already so smart, programming in really good BMS should not be much of a problem!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

0 Likes
0
1034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

Hi,

Please review Schneider Electric FAQ FA158934 "What is the expected life of my APC UPS battery?"

We do not have a chart based on load and usage. We do have runtime and efficiency charts available at http://www.apc.com/shop/ro/en/products/APC-Smart-UPS-750VA-LCD-230V/P-SMT750I

 As the FAQ lists there are many causes of battery degradation. If the load is greater than 80% and the UPS runs on battery often the battery will need to be replace sooner than the expected life. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

0 Likes
0
1034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

The Schneider "FAQs" are a good source of information.  However, for SLA batteries (in my experience) being used in most UPSs, one of the additional factors not mentioned is the "drying out" of the very small amount of electrolyte in the battery.  The  pop-valve arrangement is, by necessity very cheap and subject to production tolerances that could lead to early loss of electrolyte - especially in services where high power levels are required for "backup" at frequent occasions.  IMHO, it is time that really "smart" charging techniques be built into these "smart" UPSs that allows for 95% SOC limits to minimize "boil off" - especially if Lead acid is going to continue to be pushed for these critical systems!  As UPSs move to good BMS (battery management systems) that are absolutely required by the lithium based battery systems, this will be the needed results of long battery life and many cycles available even when "stressed to the limits" of the systems.  Just my honest opinion.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

0 Likes
0
1035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:23 AM . Last Modified: ‎2024-03-18 02:24 AM

BTW, these APC "smart" UPSs are already so smart, programming in really good BMS should not be much of a problem!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of