Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
Hello,
We have single Site setup: VMware HA Cluster protected by Single UPS configuration (Both vCenter Server and PowerChute are running on VMs). We use PowerChute 4.1 (VMware Appliance) with shutdown on event (UPS On Battery - 300 sec).
I know the shutdown sequence for this setup, it is in Application Note 180 (page 4) but i didn`t find any information about a case when the power returns during the shutdown process. What happens if the input power is restored while the shutdown process already started and PowerChute VM is not turned off yet?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
Hi,
The shutdown process will run until completed and then any power on delays will be honored prior to a restart. The UPS and the servers BIOS must be configured to power on when AC is restored for the restart to happen automatically (no user intervention).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
Hi,
The shutdown process will run until completed and then any power on delays will be honored prior to a restart. The UPS and the servers BIOS must be configured to power on when AC is restored for the restart to happen automatically (no user intervention).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
I not fully understand your reply regards to "and then any power on delays will be honored prior to a restart". Can you explain this in more detail?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
Hi,
What model UPS?
What is the model network management card?
What firmware is running on the network management card?
Depending on the UPS and NMC there are available delays for power restore state.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
UPS Model: Symmetra RM 6000
NMC Model: AP9631
NMC Firmware: v6.4.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
Hi,
Go to configure - Shutdown and you will find the start up delays. There are 2 delays Minimum Battery Capacity and Return Delay.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:27 AM . Last Modified: 2024-03-13 12:56 AM
Thank you Bill for your answers.
It will be good if in the documentation for the current or future versions of the PowerChute will be added the description for of this case.
Link copied. Please paste this link to share this article on your social media post.