we have below 3 ups
Smart-UPS VT 30 kVA
Smart-UPS RT 20000 XL
Symmetra 48K
but only 'Symmetra 48K' can return output current oid: enterprises.318.1.1.1.4.2.4.0
can ‘Smart-UPS VT 30 kVA’ and ‘Smart-UPS RT 20000 XL’ return output current via snmp ?
if yes, haw to?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
What output voltage is your Smart UPS RT providing? I only have a SURT15K and it is single phase 208V. My SURT15K UPS also only provides a general current output figure, not per phase.
Output Load: 000.6 kVA
Output Percent Load: 003 %kVA
Output Percent Power: 000 %Watts
Output Current: 0002 Amps
Output Frequency: 59.99 Hz
Current is in amps, and the description of the OID is:
The output current in 0.1 amperes drawn
by the load on the UPS, or -1 if it's unsupported
by this UPS.
So that is 14 amps you have there. This UPS does not appear to support output per phase so you only have one response is my educated guess here.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
For a lot of the three phase units, you need to look under .iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsPhase.
.1.3.6.1.4.1.318.1.1.1.9.3.3.1.4 or .iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsPhase.upsPhaseOutput.upsPhaseOutputPhaseTable.upsPhaseOutputPhaseEntry.upsPhaseOutputCurrent should work and give you three responses, one for each phase. I should clarify, depending on your location, power configuration, and number of phases, you should see at least one or more likely, multiple responses. I'd also try this for the Symmetra unit. I don't have a 48K, only a 40K and I do have the other two UPS models.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
thank you, i tried .1.3.6.1.4.1.318.1.1.1.9.3.3.1.4 and get 3 values.
but "Smart-UPS RT 20000 XL" returns 140, 0, 0, is it all right?
only one more question, what is the units for them?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
What output voltage is your Smart UPS RT providing? I only have a SURT15K and it is single phase 208V. My SURT15K UPS also only provides a general current output figure, not per phase.
Output Load: 000.6 kVA
Output Percent Load: 003 %kVA
Output Percent Power: 000 %Watts
Output Current: 0002 Amps
Output Frequency: 59.99 Hz
Current is in amps, and the description of the OID is:
The output current in 0.1 amperes drawn
by the load on the UPS, or -1 if it's unsupported
by this UPS.
So that is 14 amps you have there. This UPS does not appear to support output per phase so you only have one response is my educated guess here.