APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-29 08:26 AM . Last Modified: 2024-03-12 03:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:26 AM . Last Modified: 2024-03-12 03:03 AM
I have a Smart-UPS 1500VA (SUA1500I) and recently encounter the battery already weak and bought a new replacement battery (RBC7) to replace it.
After replace the battery and charge it for over night. I realized that the battery draining very fast, less than 30minutes (without any device using the UPS).
May I know is there any step I left out? I have tested the new battery in another working Smart-UPS, it is no problem.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
I have done the Calibration through PowerChute and it is now back to normal (tested 13% UPS Load can last around 50-60mins).
Anyways, thanks to your reply.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
Are you using PowerChute or a UPS Network Management Card? This should not be happening and you don't need to do anything after replacing a battery but we'd definitely want to look at the logs from PowerChute or the Network Management Card, if possible, to see if there is a fault or something causing this.
If it is a UPS Network Management Card you're seeing this status in, you can follow these instructions to download the logs -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&id=FA156131
If it is PowerChute, we might need to do copy paste or screenshots of the logs.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:27 AM . Last Modified: 2024-03-12 03:03 AM
I have done the Calibration through PowerChute and it is now back to normal (tested 13% UPS Load can last around 50-60mins).
Anyways, thanks to your reply.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.