how do i connect smart ups SRT5KXLI to external batteries pack SURT192XLBP

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • how do i connect smart ups SRT5KXLI to external batteries pack SURT192XLBP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
8
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

how do i connect smart ups SRT5KXLI to external batteries pack SURT192XLBP

Hi there, we have recently bought a new Smart UPS SRT 5000 (P/N: SRT5KXLI) that needs to be connected to an external batteries pack (P/N: SURT192XLBP).

the question is that whereas the batteries pack has 2 connectors the Smart UPS has only one so which of those 2 connectors should I connect to the Smart UPS?

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • srt5kxli
  • surt192xlbp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

Hi Juan,

The new SRT units are not compatible with the older SURT battery packs.  There is no cross compatibility regarding external battery packs between the SRT and SURT series.  This is because of new battery features included in the SRT including enhanced battery reporting.

Regards,

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

Hello Sir, why there is no external BP detected in my ups after I finish upgrade the firmware of ups to 4.1. Can you please help me

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

I have ups srt5000 ( srt5kxli) that need to be connected to 2 external batteries srt192bp 

The question is that whereas the batteries pack has 2 connectors and the smart ups has only one 

So witch of those connectors should i connect to the ups 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
2254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

Hi there, we have recently bought a new Smart UPS SRT 5000 (P/N: SRT5KXLI) that needs to be connected to an external batteries pack (SRT192BP).

the question is that whereas the batteries pack has 2 connectors the Smart UPS has only one so which of those 2 connectors should I connect to the Smart UPS?

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
2254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

Hi Juan,

The new SRT units are not compatible with the older SURT battery packs.  There is no cross compatibility regarding external battery packs between the SRT and SURT series.  This is because of new battery features included in the SRT including enhanced battery reporting.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:38 AM . Last Modified: ‎2024-03-18 11:05 PM

Opps.. thanks for your fast response.

could you please let me know then the part-number of the appropriate external batteries pack?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

Hi,

The battery pack SKU is SRT192BP. The runtime chart can be found on the SRT5KXLI web page. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
2254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

Hello Sir, why there is no external BP detected in my ups after I finish upgrade the firmware of ups to 4.1. Can you please help me

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 11:05 PM

Hi Lester,

What is the exact SKU of your UPS? Also, when you upgraded the firmware of the UPS is the battery pack attached?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

My question is up to how many battery packs can a Smart UPS SRT5000KXLI can support? Because i installed 2 battery packs already and on the third battery pack when I plugged the third battery pack it gives me an error of over voltage or something. Also if I update the firmware of UPS will it give the setting that i can install/mount more battery packs? Coz in the product manual i have read that it can support up to 10 battery packs.. Thank you sir..

Gerard

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
2254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

I have ups srt5000 ( srt5kxli) that need to be connected to 2 external batteries srt192bp 

The question is that whereas the batteries pack has 2 connectors and the smart ups has only one 

So witch of those connectors should i connect to the ups 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
2255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

Hi there, we have recently bought a new Smart UPS SRT 5000 (P/N: SRT5KXLI) that needs to be connected to an external batteries pack (SRT192BP).

the question is that whereas the batteries pack has 2 connectors the Smart UPS has only one so which of those 2 connectors should I connect to the Smart UPS?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore