Multiple Switched PDUs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Multiple Switched PDUs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
2
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

Multiple Switched PDUs

All,

We are building a new datacenter and I have multiple APC switched PDU's (two per rack). Each PDU is set on its own circuit breaker. I then have the servers (with mulitple power supplies) plugged into both PDU's.

My question is, how can you control (turning off, turning on, rebooting, etc) the server on mulitple PDU's. I did see in the help section about global outlets. How does this work? Also, I see that APC has the AP92200. Is this a better way to go? I know I am going to continue to get some of the switched PDU's.

Thanks for the help.

Jeff

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

One thing to note, the outlets in the group are designed to function when the PDU's themselves are powered on. If the PDU's lose power and one happens to come on before the other, the timing to power a dual power supply server will not be sync'd and if your server requires the power supplies to come "on" at the same time, this will not work for your application. You might see this in a situation where each PDU is plugged into a seperate UPS to achieve the full redundancy of using a server with the dual power supplies. However, as dirtfoot mentioned, while the PDU's are both on, the powering on, off, rebooting of outlets will be sync'd.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

Hi Jeff,
Global outlets do appear to be the solu tion you are looking for. If you configure two or more PDUs with matching multicast parameters, their outlets can be configured in global groups. Triggering a control action on the main outlet (Global Outlet) in a global group will cause all other members of that global group to behave in the same way. This would allow you to Turn off/on outlet 1 on PDU A and outlet 1 on PDU B together.

The AP92200 is a Management tool that allows you to monitor and manage all of your online APC devices, but it will not help you create the global outlets on your PDUs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

0 Likes
0
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:39 AM . Last Modified: ‎2024-03-18 04:46 AM

One thing to note, the outlets in the group are designed to function when the PDU's themselves are powered on. If the PDU's lose power and one happens to come on before the other, the timing to power a dual power supply server will not be sync'd and if your server requires the power supplies to come "on" at the same time, this will not work for your application. You might see this in a situation where each PDU is plugged into a seperate UPS to achieve the full redundancy of using a server with the dual power supplies. However, as dirtfoot mentioned, while the PDU's are both on, the powering on, off, rebooting of outlets will be sync'd.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore