Hello
I have 8 Smart-UPS RT 8000 RM XL in my Serverroom and plane to buy a power unit (with fuel) which starts after 2 minutes power down.
is there something where I must look specially for the power unti,or can I just add the max Power from each UPS to specify the Power unit.
(like 8000 VA x 8 = we need a fuel Power unit with 64kVA).
(reserves are there enaugh, each UPS has max load 50% and 2 are not in use in the moment)
thanks for answers.
Udo
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:41 AM . Last Modified: 2024-03-08 05:04 AM
Hi ich!
When you say power unit, are you talking about a generator?In general, the generator should be 3-5x the size of the total load attached to the generator (Not just the load attached to the UPS.)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:41 AM . Last Modified: 2024-03-08 05:04 AM
Hi ich!
When you say power unit, are you talking about a generator?In general, the generator should be 3-5x the size of the total load attached to the generator (Not just the load attached to the UPS.)
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.