Good morning, I have a UPS here with LED X access and two LED battery indicator access however it does not work
This being the sequence can of leds
0
1
1
0
0
What should I do?
I need that equipment
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:56 PM . Last Modified: 2024-03-06 03:28 AM
I have a same problem here, i changed batteries for a working unit but still no changes. what should we do next?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:56 PM . Last Modified: 2024-03-06 03:28 AM
Hi Andre,
This fault a lot of times points to bad batteries. How old is the unit and the batteries? Is the unit still powering your equipment? I would use a volt meter to check the voltage of the batteries. Just measure the DC voltage at the anderson connector for each of the modules. When fully charged they should be 110 volts each. Do you have another unit that uses the same batteries? If so you could temporarily borrow those.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:56 PM . Last Modified: 2024-03-06 03:28 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:56 PM . Last Modified: 2024-03-06 03:28 AM
Was placed second battery of new modules and both with a DC voltage of 108V
PERSISTS EVEN SO THE DEFECT
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:56 PM . Last Modified: 2024-03-06 03:28 AM
I have a same problem here, i changed batteries for a working unit but still no changes. what should we do next?