Is a Serial Port a Serial Port?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Is a Serial Port a Serial Port?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
5
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

Is a Serial Port a Serial Port?

I have an SC620 that just recently failed and have a few older units like a SmartUPS 1000 (Net model) as well as a 450 that I can swap in place temporarily.  But the SC620 had some proprietary systems connected to the serial port on the SC620.  

My question is will these same systems be able to communicate with the 1000 or 450 in the same manner?  In other words, do the older units 'talk' the same as the newer ones?  Or were there protocol/firmware changes on the newer ones that make them incompatible with the older ones?

Thank you in advance for any insight.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
3584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

Excellent. Thank you! At least we can be up and running with a UPS while we figure out the issue with the SC.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
3584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

Yes. All of the UPS units you have utilize the UPSlink protocol, same as your fallen SC620. They also support simple signaling if your application makes use of that instead.

Be aware that the currently produced SmartUPS (models SMT, SMX, SMC, and SURTD) product line uses a different and unfortunately not publicly documented communication protocol known as Microlink. Some of these newer models offer the ability to communicate using the Modbus protocol, which must be enabled prior to use. Modbus is available only with certain firmware revisions. There's also a legacy communications card available for the newer models having SmartSlot expansion capability. This card provides UPSlink compatible signaling. (I don't know if it supports simple signaling.)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
3584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

The spec for the UPSlink protocol has recently been officially released and can be found here: http://www.apc.com/site/support/us/en/faq/?page=content&country=ITB〈=en&locale=en_US&id=FA276164&red...

Hope this helps.

  • Tags:
  • smartlink
  • upslink
Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-12 07:45 AM

0 Likes
0
3584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-12 07:45 AM

Thank you for the reply.  One thing I should have specified is the year of the older models.  They are from the 2000s.  The face of both look like this:

Will these simply plug in and talk properly to whatever was connected to the much newer sc620?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
3584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

Hi,

The UPS image is model SU450 or SU450i and communicates using the same UPSLink protocol as the SC model. If the 1000 is model SU1000NET or SU1000NETi then it would also utilize the UPSLink protocol. 

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
3585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:57 PM . Last Modified: ‎2024-03-06 03:27 AM

Excellent. Thank you! At least we can be up and running with a UPS while we figure out the issue with the SC.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore