We have a 120 kva ups , the device is off when I on Q4s key this error appear:
CC board fault
CH board valid
Error code 1-1-5
Please help me what can I do?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:22 AM . Last Modified: 2024-03-19 02:25 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:22 AM . Last Modified: 2024-03-19 02:25 AM
Please anyone can help me... this the error no exact detail only Und. Msg. please help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:22 AM . Last Modified: 2024-03-19 02:25 AM
Hi Sara,
Check two flat cables on MIZN board for loss connection:
1- Flat cable between MIZN and DALIN (XML10-XMB16)
2- Flat cable between MIZN and ALIN (XML09-XMA07)
If they are ok i think you must replace MIZN board. After replacement you need UPS TUNER software to setup UPS.


Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:22 AM . Last Modified: 2024-03-19 02:25 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-04 12:25 AM
3N0P30047001 can you tell me this code for what
Link copied. Please paste this link to share this article on your social media post.