battery time estimation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • battery time estimation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

0 Likes
4
1411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

battery time estimation

Hi,

We just bought a UPS system for our 3 servers. 1 x SUA2200XL and 2 x UXABP48. We'd like to know how long this UPS can make our server run.

In powerchute it says we could get more than 1000 minutes of uptime, how accurate is this estimation?

Is there a way to run on batteries until they're empty and then switch on utility power so the servers don't shutdown? This way we would know how long the server survived on batteries.

Any other ways?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • PowerChute
  • shutdown
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

0 Likes
0
1411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

You're very much welcome Mathieu. Please do not hesitate to contact us if you have any issues, comments or suggestions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

0 Likes
0
1411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

Welcome to the APC Forum Mathieu.

The runtime that you see on the PowerChute software is the estimated runtime that the UPS can provide, for you to know the exact runtime on your UPS you will need to do a manual runtime calibration. Manual runtime calibration is done by making sure that there's no critical load attached to it and the UPS and external battery packs has been fully charged. Make sure as well that your UPS does have at least 30% non-fluctuating load attached to it and the proceed by unplugging the UPS and let it run on battery until it expires.

Another way of doing a calibration is by using the PowerChute Software and from there you'll be initiating a software calibration. On both calibrations you need to make sure that the internal battery of both the UPS and the external battery packs are connected. Each UXABP needs to be charged for 24 hours and needs to be charge before doing any calibration. From the software as well you need to make sure that the correct numbers of battery packs in which on your case each UXABP is equivalent to 5 battery packs already.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

0 Likes
0
1411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

In addition to what Jon said, the UPS runtime depend upon the load you plug in and the battery capacity.

Click on the below link to view the SUA2200XL estimated runtime chart:
http://www.apc.com/resource/include/ups_runtime_chart.cfm?base_sku=SUA2200XL&family_id=165

I hope that it helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

0 Likes
0
1411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

Thanks to both of you. Your answer helped us.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

0 Likes
0
1412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:49 PM . Last Modified: ‎2024-03-14 03:59 AM

You're very much welcome Mathieu. Please do not hesitate to contact us if you have any issues, comments or suggestions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore