apc suvtpf40kb4h

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • apc suvtpf40kb4h
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
geoalf
geoalf
Cadet

Posted: ‎2024-12-05 12:17 PM

0 Likes
1
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-05 12:17 PM

apc suvtpf40kb4h

hi

I have a problem after reboot of our apc it show error 

It looks like reset all data in it even SN.

SN:00000000000

Plese help where to dig in

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-01-30 05:16 AM

0 Likes
0
984
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 05:16 AM

Hello,

 

The faults appeared in the unit  are as follows:

 

-System configuration fault:

 

This event will appear if the system cannot be configured successfully, and the system will after this be locked until reboot. (The load cannot be turned on). The system startup event for system configured successfully or system configuration fault is always the first new event entry in the log after the controller is powered up.

Check and change the configuration to the system if needed.

 

-battery backup memory fault

The battery backup memory is declared faulty during system configuration, and the system is locked until reboot. (The load cannot be turned on). Note: the backup memory will always be declared faulty the first time the controller is powered up.

we recommends the PM firmware to be updated to version 7.18 and reinitialize the PM and check if the fault still appeared ,the SR needs to access the PM service port to ensure the serial number and configuration parameters are properly utilized

 

If all are set and the same issue appeared then PM controller might had a logic defection and requires the entire PM to be replaced

 

Regards,

 

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-01-30 05:16 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 05:16 AM

Hello,

 

The faults appeared in the unit  are as follows:

 

-System configuration fault:

 

This event will appear if the system cannot be configured successfully, and the system will after this be locked until reboot. (The load cannot be turned on). The system startup event for system configured successfully or system configuration fault is always the first new event entry in the log after the controller is powered up.

Check and change the configuration to the system if needed.

 

-battery backup memory fault

The battery backup memory is declared faulty during system configuration, and the system is locked until reboot. (The load cannot be turned on). Note: the backup memory will always be declared faulty the first time the controller is powered up.

we recommends the PM firmware to be updated to version 7.18 and reinitialize the PM and check if the fault still appeared ,the SR needs to access the PM service port to ensure the serial number and configuration parameters are properly utilized

 

If all are set and the same issue appeared then PM controller might had a logic defection and requires the entire PM to be replaced

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore