Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

apc smart ups 1250

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • apc smart ups 1250
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:07 AM . Last Modified: β€Ž2024-03-18 12:50 AM

0 Likes
5
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:07 AM . Last Modified: β€Ž2024-03-18 12:50 AM

apc smart ups 1250

My 1994  Smart UPS 1250 has been working since then with maybe three battery replacements.

Last week the batteries started to show exhaustion so I replaced them again. Two new 12V, 17Ah Yuasa NP17-12I went in.

Everything back together, turn the unit on , the fan runs a few seconds, then stops, the transformer makes the usual hum noise, but the front panel has no LED lights on and the two buttons have no effect whatsoever.

I am not sure if I hooked up the primary wires of the transformer correctly (White Neutral, Black Hot, Yellow Tap).

The board looks like new, no burns, no blown capacitors, no bad diodes.

Voltage between Hot and Neutral is 240Volt, between hot and Tap it is 27 Volt, transformer output is 15 Volt.

I suspect that maybe I connected the primary wires incorrectly, but do not want to try switching them without looking at a wiring schematic.

Any hint about what the problem might be? Or where I can get a schematic for this old UPS ?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:49 AM

0 Likes
0
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:49 AM

I sent a private message to you with a link to the download, see if it helps to repair πŸ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:07 AM . Last Modified: β€Ž2024-03-18 12:50 AM

0 Likes
0
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:07 AM . Last Modified: β€Ž2024-03-18 12:50 AM

hello,

Out of curiousity, why did you disconnect transformer wires? The batteries can be swapped without disconnecting any of those wires.

Transformer wirings going to PCB:
Black - XFMR-HOT
White - XFMR-NEU
Yellow - XFMR-TAP

Transformer wirings going to the heatsinks:
Black - first heatsink viewed from front of the unit
White - last heatsink viewed from front of the unit

(see attached picture of my unit)

Idr2NmBrrwE9CAMenhoZ%2BA%3D%3D.jpegIdr2NmBrrwE9CAMenhoZ%2BA%3D%3D.jpeg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:07 AM . Last Modified: β€Ž2024-03-18 12:50 AM

0 Likes
0
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:07 AM . Last Modified: β€Ž2024-03-18 12:50 AM

thanks Wolf.

since the old batteries measured both  12 Volts,  first I thought something was wrong with the MB. I disconnected the wires in order to remove the main board to check for any bad solder or damaged components.

Then I rechecked the batteries and found out they were no good when trying to recharge them with an automatic car battery charger. They did not take any charge.

I have the connections correct as I can see, but still getting no signal on the front panel. Some other component is probably gone, but hard to find without a schematic. I am working the main board 2 days now and thinking that maybe its time to trash this UPS and to get a new one.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:50 AM

0 Likes
0
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:50 AM

Check the front panel ribbon cable, it is very rigid and can be easily broken or damaged while servicing the unit. Might explain why there is no reply when you press the buttons. The next step after this would be to check the presence of +5V supply voltage of the controller logic. I could send a useful pdf to you but first I need to add you as a friend on the forums. Please approve friend request.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:50 AM

0 Likes
0
1398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:50 AM

right, when removing the MB the flat cable broke two connections, which I soldered back again and checked continuity once installed back in place. That worked correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:49 AM

0 Likes
0
1399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 07:08 AM . Last Modified: β€Ž2024-03-18 12:49 AM

I sent a private message to you with a link to the download, see if it helps to repair πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore