InRow Cooling Units Condenser's (Out Door Units) Comparison

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • InRow Cooling Units Condenser's (Out Door Units) Comparison
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

0 Likes
9
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

InRow Cooling Units Condenser's (Out Door Units) Comparison

Dear All,

I have a question regarding InRow units condensers(out door unit). As we have a range of InRow DX from 10-37kW. If we select a 30kW InRow unit with ACCD75207 (this out door unit is designed at 35 deg C) therefore, would this affect on Indoor unit efficiency? means, when the ambient temperature increases then how % of kw rating would be degraded? secondly, as we have ACCD75208 & ACCD75209 also, they both are designed at 40 & 46 deg c respectively, and also have a good price difference. but i wanna ask why we give customer generally accd75209 only bcz of higher ambient temperature or it has some other features?  why don't we give ACCD75207 because we always have N+1 Cooling redundancy in Data centers.

I will wait for your response thank u.



Thanks a lot.


Regards,

War

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

Got it! Thank u so much. U are a real knowledgeable resource.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:51 AM

Got it! Thank u so much. U are a real knowledgeable resource.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

Dear Sir,

How r u? hope fine and doing great. I have a question, May you pls let me know that the out door units like ACCD75207, 208 and 209 can be placed on two legs so that fans face would be either left or right side, for more clarify the question,  as we know these are placed on four legs(fans facing to the sky) but if i wanna place them on two legs can i place them? if no, then pls tell me the reason.

Thanks a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

Hello. These three condensers are built for vertical airflow through them (four legs, fans facing the sky). The connections to the unit are made so the hot gas goes in the top of the condenser and the condensed liquid comes out the bottom. If these units are put on their side the connections will be in the middle instead of the top and bottom. This may cause issues in the system. The only way to see if they would work horizontally is to contact your local sales and design team. They can help you configure the solution and may be able to offer other solutions to fulfill the needs of the site.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

Thank u so much dear.

I'll get back to u if i have any other question.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

Dear All,

I have a question regarding InRow units condensers(out door unit). As we have a range of InRow DX from 10-37kW. If we select a 30kW InRow unit with ACCD75207 (this out door unit is designed at 35 deg C) therefore, would this affect on Indoor unit efficiency? means, when the ambient temperature increases then how % of kw rating would be degraded? secondly, as we have ACCD75208 & ACCD75209 also, they both are designed at 40 & 46 deg c respectively, and also have a good price difference. but i wanna ask why we give customer generally accd75209 only bcz of higher ambient temperature or it has some other features?  why don't we give ACCD75207 because we always have N+1 Cooling redundancy in Data centers.

I will wait for your response thank u.



Thanks a lot.


Regards,

War

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

Hello.

     The condensers should be measured on the rating of the heat rejection and the ambient temperature that they are normally subject to. The higher the ambient temperature, the larger the condensing surface will be. This equates to a lager coil and more fans on the unit. As the ambient temperature rises, we need a larger surface to reject the heat from the refrigerant. If the surface area it too small then we will not be able to get rid of enough heat and the unit will go into high head pressure during the summer. Over-sizing the coil will waste money and could potentially cause issues if it gets to cold in the winter. The condenser should be sized to be able to reject the heat during the peak temperatures in a expected summer but not over-sized so the money is wasted. An undersized condenser will greatly reduce the capacity of the unit inside during the summer and can cause high head pressures which will shut down the cooling completely.

Thank you   

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

Dear L2,

Thanks for the provided very good info. One question I have, i.e. What is the 'Derate Factor' with respect to rising the temperature. Means, If we select ACRP102, with ACCD75207 that is designed at 35 deg.C, rated at 33kW. So, If the ambient temperature rises upto 40 deg C, in peak summer months, so how much these units would be derated? Means, from 33kW to ------??? Because, I am thinking that if one data center is running at 45kW total load. We place 3 units of ACRP with ACCD75207, So, the two cooling units which are running gives almost 60kW, If both are derated in summer season upto 5/5 kW so but still we would have 50kW, which is OK to cool down 45kW, and also we are having one other unit as standby. What do u say? This question is just for understanding. U see we have to know the 'derate factor' for clear picture. Because if derate factor is not much higher, then at least I would like to always go with ACCD75207 (if ambient temp is under control), due to compact size and lower price.

Waiting for your ever green support.

Thanks,

War

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

Hello.

The capacity rating on the condensers depends on the temperature differential (TD) between the condensing temperature and the ambient temperature. The condensing temperature of R407C is 48.8 C. So in this case the TD = 48.8 - 40 = 8.8 degrees C. The ACCD75207 will remove 4.8kw of heat per 1 degree C. This means it will remove 4.8 x 8.8 = 42.24 kw of heat. If the ambient temp raises to 45 degree C then TD = 48.8 - 45 = 3.8 x 4.8kw/1c = 18.24 Kw. This does drop of steeply as the ambient temperature rises. The ACCD75208 will remove 8.1kw per 1 degree C, while the ACCD75209 will remove 11kw per degree C. The condensing temperature is the same on all the condenser. If this need more explanation please let us know.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:07 AM . Last Modified: ‎2024-03-18 12:50 AM

WOW SIR...... Amazinggggg..... Detailed, neat & clean and right on target explanation. You taught me just like a teacher, a good one.

Only one thing is still confusing, i.e. U said " This means it will remove 4.8 x 8.8 = 42.24 kw", But in the file (pls download from below link) at page no. 28, under the heading of air cooled performance calculation, at 33 °C it gives 33.7kW. That is why i couldn't understand that how it would give 42.24kW.  Secondly plz see page no. 35, Under the heading of 'Mechanical Data', ACCD75207 shows, kW/°C TD is 9.3kW. What does it mean? i couldn't understand?? Same question is for ACCD75208 and 209 respectively.

https://app.box.com/s/qw5cn2fk5c22dwnwpiio

I will wait for your response. Thank  you.

Regards,

War

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of