APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-28 09:52 PM . Last Modified: 2024-03-14 11:32 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:52 PM . Last Modified: 2024-03-14 11:32 PM
Hi All
This is on a Symmetra 40K UPS. We have the following error
Critical - UPS: A runtime alarm threshold violation exists.
The UPS is down to 2 minutes now, is this error just the fact that its only has 2 mins runtime or could this be something else ?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:52 PM . Last Modified: 2024-03-14 11:32 PM
yep so if you adjust that setting the violation should clear (or if you add more batteries i guess).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:52 PM . Last Modified: 2024-03-14 11:32 PM
okay so it seems like you have a runtime threshold configured in the network management card under the UPS tab->Configuration->Power. this is worded as Alarm If Runtime Under: xxx
what is this value set to? do you know why your runtime is so low?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:52 PM . Last Modified: 2024-03-14 11:32 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:52 PM . Last Modified: 2024-03-14 11:32 PM
Ah its set to 5mins so that will explain it. A lot of Extra load has been put on it so its dropped runtime quite a bit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:52 PM . Last Modified: 2024-03-14 11:32 PM
yep so if you adjust that setting the violation should clear (or if you add more batteries i guess).
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.