Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Wrong SysObjectID returned in Solarwinds for AP9617 and SmartUPS 1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Wrong SysObjectID returned in Solarwinds for AP9617 and SmartUPS 1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:28 AM

0 Likes
3
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:28 AM

Wrong SysObjectID returned in Solarwinds for AP9617 and SmartUPS 1500

I have several SmartUPS 1500 equipped with AP9617.

I am trying to get Solarwinds Orion's Network Performance Monitor to manage these UPS.

However, Solarwinds reports SysObjectID to be 1.3.6.1.4.1.318.1.3.2.7 which is for a SmartUPS 450.

The correct SysObjectID should be 1.3.6.1.4.1.318.1.3.2.16

I am concerned that if the SysObjectID is wrong, what else is not correct.

I contacted Solarwinds they told me this is a APC issue.

I have downloaded the latest MIB from APC (powernet409.mib)

Solarwinds told me very clearly that Updating Orion MIB does not change the way NPM polls data from the device.

I was instructed to get a proper OID for my combination of network card and UPS.

HELP!

Bryan Smith

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9617
  • smartups_1500
  • solarwinds
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:27 AM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:27 AM

Hi again,

This particular thing is a UPS issue. So a newer card will still show the same thing.

There is nothing else critical off the top of my head that I can think of that has a quirky bug like this. For stuff like runtime, that is also reported from the UPS itself but that is typically a good estimate and when it goes on battery, it becomes more and more accurate. That applies in general with or without a management card regarding what I just noted on the runtime. Also for runtime, you see the same thing via SNMP that you'd see via the web and telnet/SSH interfaces.

If you run into any other issues or have any further questions, let me know. Hope you have a nice weekend! laughing

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:28 AM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:28 AM

Thank you, Angela for your speedy reply!

I believe I can correct the UPS Machine Type by editing Solarwinds and cheating by keying the correct SysObjectID for a 1500.

Correcting the Model Number for some of my users (like the boss) that might freak out some when they expect a 1500 and only see a 300.

I am more concerned about it the other data correct...like Battery Run Time?

Just curious: I know my network cards are older, so would a newer network card solve this issue...or is this a UPS issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:27 AM

0 Likes
0
1611
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:27 AM

Hello,

This issue has been around for a while. Certain model UPSs used to report back incorrectly as Smart UPS 450 when that is not really what they are. The root problem is certain older model UPSs and unfortunately, the UPSs are not firmware upgradeble themselves to fix it.

Are you just interested in what UPS typemodel it is? Older UPSs that you could be using AP9617 with are unable to report their exact SKU but your next best option will be .iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsIdent.upsBasicIdent.upsBasicIdentModel which is .1.3.6.1.4.1.318.1.1.1.1.1.1.

My UPS does the same yours does - sysObjectID comes back as enterprises.apc.products.system.smartUPS.smartUPS450 and the OID I just gave you comes back as Smart-UPS 3000 RM. They must map to different values on the UPS EEPROM.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:27 AM

0 Likes
0
1612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:27 AM

Hi again,

This particular thing is a UPS issue. So a newer card will still show the same thing.

There is nothing else critical off the top of my head that I can think of that has a quirky bug like this. For stuff like runtime, that is also reported from the UPS itself but that is typically a good estimate and when it goes on battery, it becomes more and more accurate. That applies in general with or without a management card regarding what I just noted on the runtime. Also for runtime, you see the same thing via SNMP that you'd see via the web and telnet/SSH interfaces.

If you run into any other issues or have any further questions, let me know. Hope you have a nice weekend! laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore