Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

How to improve runtime accuracy for different models of APC

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to improve runtime accuracy for different models of APC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:28 AM

0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:13 AM . Last Modified: ‎2024-03-05 02:28 AM

How to improve runtime accuracy for different models of APC

In our production system, we have over 100s of APC UPS's all varying models some SUA ,some smart UPS, 1kva, 2.2kva, and 5kva. They range in 1 year old to some over 10 years. All of them show different runtimes, and during actual power outages the APC UPS did not hold up to the displayed runtimes by an factor of over 60%. To improve the accuracy of the runtime ( i can tolerate within 10 % of stated runtime)  and by reading through various APC literature, and advice from engineers, I have come to the following conclusions:

1. Replace UPSes every 6 to 8 years.

2. Replace Batteries every 3 to 5 years,  more sooner for closets running hotter.

3. Do runtime calibration every 6 to 12 months. ( Doing this more often, will reduce the life of the battery, was what i heard.  Not sure if doing this "runtime calibration" can knock out power to production systems, when we do this, and if certain models can handle this better than other. Plus if there an automated way to do this for the 100s of UPS, and schedule them in groups - that would be awesome).

4. Buy only smart UPS models or Symmetras ( As they can do calibration better, and are more accurate).

5.  Upgrade to new NMC 30 or 31 model - and with version 6.0.6.

6. Run at 30 to 40% load or less. ( we normally run at around 20 to 25% load).

Do these conclusions hold good ? Are others replacing Batteries and UPSes at this rate ?

Finally, do all these make good standards for standard IT closets - which we try to keep at room temperature of around 70 F, but some run hot at 85 to 90 , due to numerous running equipment and not having sufficient cooling in the closets.

Thanks for shedding light on this.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore