Wrong RPDU SNMP reply

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Wrong RPDU SNMP reply
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

0 Likes
5
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

Wrong RPDU SNMP reply

Dear all,

Please advice whats wrong:

AP8881 PDU connected with 3 other via NPS

When I do SNMP get for power counters the wrong PDU replies:

[root@cacti ~]# snmpget -c public -v1 -On 172.27.4.3 .1.3.6.1.4.1.318.1.1.26.4.3.1.5.1
.1.3.6.1.4.1.318.1.1.26.4.3.1.5.1 = INTEGER: 112
[root@cacti ~]# snmpget -c public -v1 -On 172.27.4.3 .1.3.6.1.4.1.318.1.1.26.4.3.1.5.2
.1.3.6.1.4.1.318.1.1.26.4.3.1.5.2 = INTEGER: 15
[root@cacti ~]# snmpget -c public -v1 -On 172.27.4.3 .1.3.6.1.4.1.318.1.1.26.4.3.1.5.3
.1.3.6.1.4.1.318.1.1.26.4.3.1.5.3 = INTEGER: 14
[root@cacti ~]# snmpget -c public -v1 -On 172.27.4.3 .1.3.6.1.4.1.318.1.1.26.4.3.1.5.4
.1.3.6.1.4.1.318.1.1.26.4.3.1.5.4 = INTEGER: 120

RPDU group screenshot:

Did APC changed something in OIDs?

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap8881
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

thanks for reply but that is not comfortable way. If someone reorder DisplayID than need to change OIDs in all monitoring systems.

Better not touch Display IDs since PDU group powered on.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

I'm not familiar with the RPDUs but I took a look at the MIB and noticed the table contains OIDs that describe which RPDU each table entry corresponds with.

You're currently looking at:

.1.3.6.1.4.1.318.1.1.26.4.3.1.5

You might consider also looking at:

.1.3.6.1.4.1.318.1.1.26.4.3.1.2

and

.1.3.6.1.4.1.318.1.1.26.4.3.1.3

to determine the corresponding RPDU module for the table index.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

Agree with voidstar. The SNMP indexes may not be the same as the display ID since the user can change the display ID after power up. As voidstar mentioned, you should check the index table with the specific OID mentioned. If it is confusing, you'd have to reset the indexes or you can change the module IDs around to match the index. I believe to reset the indexes it could be painful and require a reset to defaults and playing around with the group communication (removing PDUs and re-adding them, etc).

There is a bit of a note on that topic here -> http://www.apc.com/us/en/faqs/FA164436

Network Port Sharing and SNMP Polling

All Rack PDUs in a group can be accessed through the Host Rack PDU via SNMP "rPDU2" OIDs available in our PowerNet MIB.

Note: PowerNet MIB v4.0.6 or higher is required for use with SNMP and a Network Port Sharing enabled device.

The full path to these OIDs is:
iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).rPDU2(26)

Individual Rack PDUs can be identified in the SNMP MIB tables by viewing the corresponding "Module" OIDs in each table. These Module OIDs will return the Display ID of the Rack PDU.

Example Module OIDs: rPDU2IdentModule, rPDU2DeviceConfigModule, rPDU2SensorTempHumidityConfigModule

In order to be backwards compatible with previous versions, the Host Rack PDU will always be the first index in any table that supports multiple Rack PDUs. In addition, after the Rack PDU group is set up, the index order of guest Rack PDUs should not change even if the Display ID is changed or a PDU temporarily loses communication. The index order should only change if you manually remove a Rack PDU from the group. A MIB table walk should skip the indexes associated with a Rack PDU that has temporarily lost communication.
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

As I understand there is no any OID to get SNMP power counters by DisplayID?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

There is by way of a relational join, you need to get:

.1.3.6.1.4.1.318.1.1.26.4.3.1.5.x

where .1.3.6.1.4.1.318.1.1.26.4.3.1.2.x == DisplayID

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

0 Likes
0
991
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:37 PM

thanks for reply but that is not comfortable way. If someone reorder DisplayID than need to change OIDs in all monitoring systems.

Better not touch Display IDs since PDU group powered on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of