ATS on single UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • ATS on single UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

0 Likes
3
915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

ATS on single UPS

I have one question. 

Can one ATS be connected to two different PDUs that are then connected to a single Symmetra 160K UPS? 

If I take out one power supply from ATS will it still provide power from another?

Thank you

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ats
  • power
  • supply
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

0 Likes
0
915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

The ATS has 2 DC power supplies, one powered by each source. If one of the power supplies is bad, when the source with the good supply drops, the ATS will lose power and will drop the load even though the other source is OK. However, a bad DC supply should raise an alarm. You could look in device status and see if it reports them both as OK.

It is good practice to have both sources on the same phase (the ATS will report "Phase sync: In sync"). Due to how fast the ATS needs to operate when switching sources, it is possible for both sources to be briefly connected due to physical delays in the relays in the ATS. If the sources are out of sync, unpleasant things can happen. That's also the reason for the warning to disconnect one source when updating the ATS firmware. If it is appropriate in your situation, you can also configure "Preferred source: None" which will prevent an un-necessary transfer back to the preferred source once that source is providing power again.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

0 Likes
0
915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

It doesn't really matter how you supply power to the ATS inputs, as long as one of them has power that is within tolerance it will be routed to the output.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

0 Likes
0
915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

That's what I thought. But funny thing happened. When I pulled out one power supply all equipment turned off and the ATS was powered. Is it maybe something with the ATS itself (hardware wise) or can be something with the configuration? 

  • Tags:
  • ats
  • power
  • switch
Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

0 Likes
0
916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:09 AM . Last Modified: ‎2024-03-18 11:38 PM

The ATS has 2 DC power supplies, one powered by each source. If one of the power supplies is bad, when the source with the good supply drops, the ATS will lose power and will drop the load even though the other source is OK. However, a bad DC supply should raise an alarm. You could look in device status and see if it reports them both as OK.

It is good practice to have both sources on the same phase (the ATS will report "Phase sync: In sync"). Due to how fast the ATS needs to operate when switching sources, it is possible for both sources to be briefly connected due to physical delays in the relays in the ATS. If the sources are out of sync, unpleasant things can happen. That's also the reason for the warning to disconnect one source when updating the ATS firmware. If it is appropriate in your situation, you can also configure "Preferred source: None" which will prevent an un-necessary transfer back to the preferred source once that source is providing power again.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of