Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Windows Error Log show many Event ID 61456 "APC UPS Service" no Connection
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2902:02 AM. Last Modified: 2024-03-1304:26 AM
Windows Error Log show many Event ID 61456 "APC UPS Service" no Connection
Hello,
I have many Errors (between 1 and 10 per day) in my Windows Log on SBS 2008 with PowerChute. Then I open the Program by clicking on tray icon everything seems to be all right. There are no events for the last 24 weeks.
Does anybody else has this problem?
Should I upgrade to PowerChute Personal Edition V3.0.2? Is this version ok for SBS 2008?
Thank you very much!
Philipp
This is the Data from APC PowerShut Software:
Modell: Back-UPS RS 1500 LCD Seriennummer: JB0827009086 Firmwareversion: 849.H1 .I Datum des letzten manuellen Selbsttests: 08.02.2016 Ergebnis des letzten Selbsttests: Bestanden RAM: 32 GB Freier Speicherplatz auf der Festplatte: 21.961 MB Softwareversion: PowerChute Personal Edition 2.1.1
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2902:02 AM. Last Modified: 2024-03-1304:26 AM
Hi,
The error indicates that PowerChute cannot communicate with the UPS. This can be caused by a momentary interruption on the system Universal Serial Bus (USB).
Since you are running an older version you could upgrade to 3.0.2 to see if the errors subside but if the issue is due to a system fault upgrading the software will not help.
We have not specifically tested SBS 2008 with PCPE 3.0.2 but I think it should work. You can download any of the listed installers i.e. Windows 7, 8, 10. All of the installers are the same.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2902:02 AM. Last Modified: 2024-03-1304:26 AM
Hi,
The error indicates that PowerChute cannot communicate with the UPS. This can be caused by a momentary interruption on the system Universal Serial Bus (USB).
Since you are running an older version you could upgrade to 3.0.2 to see if the errors subside but if the issue is due to a system fault upgrading the software will not help.
We have not specifically tested SBS 2008 with PCPE 3.0.2 but I think it should work. You can download any of the listed installers i.e. Windows 7, 8, 10. All of the installers are the same.