Will my APC Smart-UPS 1250 120V work with the new Power Chute USB?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Will my APC Smart-UPS 1250 120V work with the new Power Chute USB?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
7
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

Will my APC Smart-UPS 1250 120V work with the new Power Chute USB?

I have had this AP1250 APC Smart-UPS 1250 120V since the early 90's. I have replaced the batteries twice in all these years. It works perfectly but I'd like to 'manage' it. Can I use the new Power Chute personal program to manage it online? I'm running XP-SP2. I also have a USB adapter that will connect to the serial port on the rear of the unit. The only selections on the XP UPS management configuration screens are for Com 1,2,3,4 and no USB ports are listed. Will installing the new Power Chute Personal 2.0 allow me to use the USB port? This model is so old, it is not listed anywhere.

I have the original software (Power Chute 5.2.3) but it is not currently installed.

Thanks,

Mick

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

Thanks!! I'm pretty sure this Smart 1250 was built in the late 80's πŸ™‚
I'll update with any progress I make.

Mick

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

The main reason I recommended the upgrade, is like I stated before. I don't think the UPS is capable of communicating with a software package like PCBE. You're looking at using a UPS that was manufactured probably in 1995/1996 or earlier, with a software package that was released around 2000.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

Kevin,
I never asked about Business Edition software.......I'm pretty sure PowerChute came with this
UPS. Why would I want to upgrade? It's working great. πŸ™‚

Mick

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

PCPE 2.0 will not support USB Smart-UPS.

You would have to use PowerChute Business Edition, but the likelihood that the UPS is supported by that software, due to age, is very minimal.

If you would like to continue using software with the UPS, it may be time to replace the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

bmwmick wrote:
I have had this AP1250 APC Smart-UPS 1250 120V since the early 90's. I have replaced the batteries twice in all these years. It works perfectly but I'd like to 'manage' it. Can I use the new Power Chute personal program to manage it online? I'm running XP-SP2. I also have a USB adapter that will connect to the serial port on the rear of the unit. The only selections on the XP UPS management configuration screens are for Com 1,2,3,4 and no USB ports are listed. Will installing the new Power Chute Personal 2.0 allow me to use the USB port? This model is so old, it is not listed anywhere.

I have the original software (Power Chute 5.2.3) but it is not currently installed.

Thanks,

Mick
Not all serial converter works. My Belkin works. The cheapo I got from eBay, no. Once you have it installed properly and it is in working orders, it will actually become one of the COM ports and be assigned a COM number, so if it's assigned 4, you choose COM4 in Windows UPS management and choose APC, Smart-UPS. When you hit apply, you know your UPS is talking to the computer when Status window becomes filled in.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

I'm not 100% positive on this, but the primary factor here is not whether or not the USB converter works, it's that PCBE probably won't see a 1st or 2nd generation Smart-UPS. They were never compatible, as PowerChute Plus was the software prior.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

KV,
You are correct, I can assign whatever COM port I want to the USB converter.
I'm pretty sure PowerChute should work if the USB converter works. Now, do I
have to use the 940-0024 cable too? I have ways of re-assigning the pins if I want.

I'm thinking, if the converter works on the UPS port, and XP recognizes the UPS
(in power tab) as being on Com-4, XP should have control of the UPS and I won't need
to mess with PowerChute at all.

Thanks,
Mick

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

0 Likes
0
2009
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 07:42 AM . Last Modified: β€Ž2024-03-07 10:47 PM

Thanks!! I'm pretty sure this Smart 1250 was built in the late 80's πŸ™‚
I'll update with any progress I make.

Mick

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore