Why doesn't my NMC accept my SSL certificate?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Why doesn't my NMC accept my SSL certificate?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
0
980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

Why doesn't my NMC accept my SSL certificate?

I have am working with a new AP9631 NMC2. See here for product page: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP9631&tab=documentation

There is a document called "Security Handbook Network Enabled Devices AOS V.6.X.X" on the documentation page.  I've been following the section entitled "Create a Server Certificate and Signing Request" trying to install a signed SSL certificate on the NMC.   I have not yet succeeded. 

When I get to the instruction to "Send the certificate signing request to...a Certificate Authority managed by your own company or agency" I use the following command to get the certificate signed by our Certificate Authority:

certreq -submit -attrib "CertificateTemplate:WebServer"


(see this Microsoft technet article for details Appendix 3: Certreq.exe Syntax)


That works and a signed certificate is issued by our Certificate Authority and I continue to follow the instructions in the "Import the signed certificate" subsection.  The first sign that there is a problem occurs when I get to the subsection entitled "Load the Server Certificate to the Management Card or Device".

Specific Symptom

When I select "Add or Replace Certificate File", the web interface hangs for about a minute and then shows an updated "Certificate" page.  On that page, it shows

Status: Valid Certificate

The problem is that when I click on valid certificate, the installed certificate is an internally generated certificate (i.e. OU= "American Power Conversion Corp"), not the certificate I just tried to add.  A similar thing happens if I upload the certificate using FTP.  I have checked the fingerprints of the internally generated certificate from attempt to attempt: They are diffferent.  It seems that during the minute the web interface hangs, the NMC is generating a new certificate.

Why isn't the NMC2 accepting my SSL certificate and instead internally generating a new certificate?

APC Models and Versions


APC Security Wizard version: 1.04

Hardware Factory

Model Number: AP9631

Serial Number: ZA1324021754

Hardware Revision: 05

Manufacture Date: 06/15/2013

MAC Address: 00 C0 B7 B4 15 26

Management Uptime: 0 Days 0 Hours 5 Minutes

Application Module

Name: sumx

Version: v6.0.6

Date: Apr 5 2013

Time: 11:25:39

APC OS (AOS)

Name: aos

Version: v6.0.6

Date: Apr 5 2013

Time: 10:36:37

APC Boot Monitor

Name: bootmon

Version: v1.0.2

Date: Jan 21 2010

Time: 13:35:57

About UPS

Model: Smart-UPS RT 2200 XL

Position: RACK

Serial Number: QS1323140847

Firmware Revision: 802.5.D

Manufacture Date: 06/04/13

Other Versions

Certificate Authority: Windows Server 2012R2 Active Directory Certificate Services

Certificate Authority Type: Enterprise Subordinate

Web Browser: Firefox 27.0.1

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore