Resetting battery constant values whilst unit has NMC installed

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Resetting battery constant values whilst unit has NMC installed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

0 Likes
2
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

Resetting battery constant values whilst unit has NMC installed

Hello,

We have several SUA3000RMI2U units installed with a AP9630 NMC installed, prior to this we were just using Serial communications to monitor the UPS and we could stop the APC service and run Hyperterminal/Putty to update the battery constant values.

Since installing the NMC we have been unable to update battery constant values either via NMC Serial or via UPS Serial port.  The work-a-round is to shutdown the UPS and remove the NMC and communciate via Serial to update the values.  As you could imagine, this requires outages to be arranged and causes further down time.

I am hoping that there is a better solution without having to shutdown the UPS and remove the NMC, has anyone else had this issue?  I have looked through the CLI manual but could not find any information regarding battery constants updating.

I hope the power of the community would be able to offer some solutions.

Thanks in advance.

Regards,

Justin

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

I have been successfully removing and re-inserting many different models of NMC card into Smart-UPS that are powered up/online for years now (per Angela N's guidance comments) and as long as its done a certain way it has proven to be safe: I have made a practice of doing the unplugging and re-insertion as quickly and as solidly as possible. IE for removal I undo the screws holding the NMC in, and rather than fiddle with a screwdriver around the edges of the card to pry the card out which might result in the card flopping around in the connector and making/breaking connection erratically, I just grab onto and use the network cable and/or temperature probe cables (IE leave the cables plugged into the card) to pull the card out quickly - there is not much resistance disconnecting the card from the smartslot so no risk of damaging the cables or the RJ connector. On RE-Insertion again I insert the card as quickly as possible into the smartslot - straight in with no hesitation.


See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

You can just hot-swap (or uninstall/reinstall) the NMC. The Smart UPS user's guides all say to power down and "braindead" the system but I really think they just haven't updated that part in ages. I can't remember the last time I did that to install/uninstall a management card and the risk of anything happening is so slim since all of the more modern UPSs and NMCs, are designed to be hot swappable anyway. I only would suggest following this procedure if there is something odd going on - UPS is smoking, melting, etc and I would hope at that time, you wouldn't be focused on installing the NMC anyway wink The downtime is not worth it - I agree.

"Updating battery constants" is not an officially recommended procedure so you won't find any documentation about it anywhere besides the internet. The recommended solution is when you replace your batteries, to do a runtime calibration via software/NMC or manually to update the runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:23 AM . Last Modified: ‎2024-03-05 01:36 AM

I have been successfully removing and re-inserting many different models of NMC card into Smart-UPS that are powered up/online for years now (per Angela N's guidance comments) and as long as its done a certain way it has proven to be safe: I have made a practice of doing the unplugging and re-insertion as quickly and as solidly as possible. IE for removal I undo the screws holding the NMC in, and rather than fiddle with a screwdriver around the edges of the card to pry the card out which might result in the card flopping around in the connector and making/breaking connection erratically, I just grab onto and use the network cable and/or temperature probe cables (IE leave the cables plugged into the card) to pull the card out quickly - there is not much resistance disconnecting the card from the smartslot so no risk of damaging the cables or the RJ connector. On RE-Insertion again I insert the card as quickly as possible into the smartslot - straight in with no hesitation.


Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore