Continuously kicked out of AP9631 management website

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Continuously kicked out of AP9631 management website
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
5
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

Continuously kicked out of AP9631 management website

I hope someone can shed some light on this issue I have!

I have installed 4 new UPS, 2X SMX2000RMLV2UNC and 2X SURT6000RMXLT3U with AP9631 management cards.

I built up the config on the first one and created a config file I used to deploy the others.

Last week, everything was working fine.

We turned them on last weekend, and now, I get continuously kicked out of the management website. It takes less than a minute and I'm out, no error message, nothing.

When I try to log in, I get the message that another user is logged in already. Then I have to go to loginpage/logout.htm to log out and log back in.

I tried with bot IE10 and Chrome, same problem.

And as I am typing this message, the problem seems to have corrected itself and I do not get errors any longer...

Has anyone ever experienced this problem?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
0
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

This does not happen all that regularly without some type of cause - I mean one hang up once in a while here and there I may expect but nothing too frequent.

Can you give me the event.txt from the Network Management Card to review please?

Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
0
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

I hope someone can shed some light on this issue I have!

I have installed 4 new UPS, 2X SMX2000RMLV2UNC and 2X SURT6000RMXLT3U with AP9631 management cards.

I built up the config on the first one and created a config file I used to deploy the others.

Last week, everything was working fine.

We turned them on last weekend, and now, I get continuously kicked out of the management website. It takes less than a minute and I'm out, no error message, nothing.

When I try to log in, I get the message that another user is logged in already. Then I have to go to loginpage/logout.htm to log out and log back in.

I tried with bot IE10 and Chrome, same problem.

And as I am typing this message, the problem seems to have corrected itself and I do not get errors any longer...

Has anyone ever experienced this problem?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
0
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

I validated, I am also on v5.1.7 thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
0
1678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

This does not happen all that regularly without some type of cause - I mean one hang up once in a while here and there I may expect but nothing too frequent.

Can you give me the event.txt from the Network Management Card to review please?

Instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
0
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

Here is the copy of the log from today and yesterday, I'm MC6

I think I found out what is happening, looks like I have two ip right now on my PC and it's logging from different IPs!

I disabled my wifi link, I'll check out to see if it fixes the issue.

Thanks!

DateTimeEventCode
19.02.201415:32:51System: FTP user 'apc' logged in from 10.248.12.76.0x0016
19.02.201411:38:25System: Web user 'mc6' logged out from 10.248.12.76.0x001F
19.02.201411:28:20System: Web user 'mc6' logged in from 10.248.12.76.0x0015
19.02.201410:45:44System: Web user 'mc6' logged out from 10.248.12.76.0x001F
19.02.201410:26:24System: Web user 'mc6' logged in from 10.248.12.76.0x0015
19.02.201408:23:11System: Web user 'mc6' logged out from 10.248.16.129.0x001F
19.02.201408:11:42System: Web user 'mc6' logged in from 10.248.16.129.0x0015
19.02.201408:07:28System: Web user 'mc6' logged out from 10.248.12.76.0x001F
19.02.201407:57:00System: Web user 'mc6' logged in from 10.248.12.76.0x0015
18.02.201416:20:23System: Web user 'mc6' logged out from 10.248.16.129.0x001F
18.02.201416:20:17System: Configuration change. Email 'from' address.0x0033
18.02.201416:19:50System: Web user 'mc6' logged in from 10.248.16.129.0x0015
18.02.201414:23:10System: Web user 'mc6' logged out from 10.248.12.76.0x001F
18.02.201414:13:01System: Web user 'mc6' logged in from 10.248.12.76.0x0015
18.02.201413:26:59System: Web user 'mc6' logged out from 10.248.12.76.0x001F
18.02.201413:26:30System: Web user 'mc6' logged in from 10.248.12.76.0x0015
18.02.201413:20:03System: Web user 'mc6' logged out from 10.248.16.129.0x001F
18.02.201413:09:55System: Web user 'mc6' logged in from 10.248.16.129.0x0015

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

0 Likes
0
1677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:16 AM . Last Modified: ‎2024-03-05 01:37 AM

Thank you - and yes, I agree, multiple sessions! Let's monitor and let me know if you think it is related to something else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore