Why does galaxy 3500 goes into internalbypass mode when three phase supply is lost?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Why does galaxy 3500 goes into internalbypass mode when three phase supply is lost?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
aelma93
aelma93
Cadet

Posted: ‎2025-03-02 01:06 PM

0 Likes
1
539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-02 01:06 PM

Why does galaxy 3500 goes into internalbypass mode when three phase supply is lost?

 

Current have 7 galaxy 3500 10KVA installed as backup supply for 7 substation.

The UPSs are installed in a dual supply manner, 3 phase supply and single phase bypass supply. 

We currently have a 2 monthly load test on the UPS, where the load test is completed by turning off the 3 phase supply to the UPS, whilst single phase supply is available. This is to simulate a power loss, whilst also keeping the single phase available for internalbypass incase any issues with the UPS. 

The following was noted:

  • some UPS goes into battery mode (as expected)
  • whilst some UPS goes into bypass mode

 

why is this?, is this a configuration issue?, where can I get full configuration manual. The current available installation and operation manuals dont have anything regarding this.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-03-07 05:40 AM

1 Like
0
503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-07 05:40 AM

Hello,

 

In order to investigate this issue,you can provide a picture of  the raw status data from display to verify if there a hardware issue appeared in the unit power module,since your are performing load bank test,it might the UPS in  Bypass due to fault, Over load

 

UPS in Bypass due to fault, may be found during over loads. Check for over loads on the UPS, check for balanced loading across all three phases. Check application the UPS is being used in such as to support motor loads, printers or other equipment that may draw an inrush current.
 
Often times if motor type loads are being used you can get High DC events and transfers to bypass or load dumps as a result. The UPS is not really rated for motor type loads as the UPS inverter is rated for kVA, not kW. Other words the UPS is not fully rated output and the inrush that is characteristic of motor loads can cause over load of the inverter.
 
If the SUVT gets an high inrush current on the output and bypass voltage is available it will swap to bypass operation using the internal Static bypass switch (SCR's). 
 
If load is dropped and cause of output over error is not associated with a Low DC battery event, over load or High DC event then replace the Power Module, otherwise it is a normal system behaviors during overloads to turn on static bypass operation 
 
Regards,
Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-03-07 05:40 AM

1 Like
0
504
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-07 05:40 AM

Hello,

 

In order to investigate this issue,you can provide a picture of  the raw status data from display to verify if there a hardware issue appeared in the unit power module,since your are performing load bank test,it might the UPS in  Bypass due to fault, Over load

 

UPS in Bypass due to fault, may be found during over loads. Check for over loads on the UPS, check for balanced loading across all three phases. Check application the UPS is being used in such as to support motor loads, printers or other equipment that may draw an inrush current.
 
Often times if motor type loads are being used you can get High DC events and transfers to bypass or load dumps as a result. The UPS is not really rated for motor type loads as the UPS inverter is rated for kVA, not kW. Other words the UPS is not fully rated output and the inrush that is characteristic of motor loads can cause over load of the inverter.
 
If the SUVT gets an high inrush current on the output and bypass voltage is available it will swap to bypass operation using the internal Static bypass switch (SCR's). 
 
If load is dropped and cause of output over error is not associated with a Low DC battery event, over load or High DC event then replace the Power Module, otherwise it is a normal system behaviors during overloads to turn on static bypass operation 
 
Regards,
Karim
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore