Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:56 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:56 AM
I just purchased some NetShelter SX enclosures for a new blade server deployment. I had planned to run inter-enclosure cabling in bundles under the raised floor. But, my co-location provider will not allow me to put anything below the floor and I cannot expose any cables outside my enclosures, e.g. overhead ladder rack.
I can remove the side panels between adjacent enclosures. Are there other options? I am concerned that removing side panels may impact airflow and cause a heat issue inside my enclosures.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:55 AM
If on the roof as clarkson suggested is not an option for you (you could screen from front and rear view the roof-top cables by using data cable partitions--parts such as [AR8162ABLK|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AR8162ABLK]), then you could replace the side panels that come with the NetShelter with the Split Feed Through Side Panels, such as [AR7305|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AR7305&tab=models]. (buzz)
Message was edited by: joeledesma
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:00 AM . Last Modified: 2024-03-18 02:55 AM
If on the roof as clarkson suggested is not an option for you (you could screen from front and rear view the roof-top cables by using data cable partitions--parts such as [AR8162ABLK|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AR8162ABLK]), then you could replace the side panels that come with the NetShelter with the Split Feed Through Side Panels, such as [AR7305|http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AR7305&tab=models]. (buzz)
Message was edited by: joeledesma
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.