Posted: 2021-07-01 06:27 AM . Last Modified: 2024-03-04 11:35 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 06:27 AM . Last Modified: 2024-03-04 11:35 PM
We are a Digital Controls Group specializing in high level automated buildings on one the largest research campuses in the nation. We have field devices that perform smoke control functions and supervisory devices that send fire and security notifications from over 100 subnets. We typically use an APC Smart UPS 750 to supply power to these field devices of which we have between 50 and 100 in the field. What we do not have is a good way to monitor them. I have recently started to determine the best course for monitoring these devices. Our field devices themselves have a battery backup and will perform a proper shutdown upon loss of power
therefore we do not need to have applications telling our devices/PCs to shut down. I am hoping to use something like Power Chute or some other app to monitor the Smart UPS 750s and the few other APC UPS devices. I have set one Smart UPS 750 up to send email notifications and that works however it cannot send out a notification if it is offline where a central server could. I am looking for the best option for a situation like ours where we only need to monitor the UPS and not have it shut down a PC/Server.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 06:27 AM . Last Modified: 2024-03-04 11:35 PM
Sorry for the delay in response.
Since you don't need to have any PCs involved, it may be best to look into Network Management Cards in each UPS (which go into the UPS SmartSlots) and then potentially StruxureWare Data Center Expert (http://www.apc.com/products/family/index.cfm?id=350) to monitor all of the Network Management Cards in your UPSs (which it does via SNMP). This assumes that network monitoring is the route you want to go versus something like dry contacts for monitoring. All of the UPS management options are available here- > APC Product Information for Uninterruptible Power Supply (UPS) <meta http-equiv="Content-Type" /> - ...
I hope this helps get you started. Let me know if you have any other questions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 06:27 AM . Last Modified: 2024-03-04 11:35 PM
Sorry for the delay in response.
Since you don't need to have any PCs involved, it may be best to look into Network Management Cards in each UPS (which go into the UPS SmartSlots) and then potentially StruxureWare Data Center Expert (http://www.apc.com/products/family/index.cfm?id=350) to monitor all of the Network Management Cards in your UPSs (which it does via SNMP). This assumes that network monitoring is the route you want to go versus something like dry contacts for monitoring. All of the UPS management options are available here- > APC Product Information for Uninterruptible Power Supply (UPS) <meta http-equiv="Content-Type" /> - ...
I hope this helps get you started. Let me know if you have any other questions.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.