What fuse do I need on the batteries of a SmartUPS 1400 ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What fuse do I need on the batteries of a SmartUPS 1400 ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
5
2550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

What fuse do I need on the batteries of a SmartUPS 1400 ?

Say all!
I looked EVERYWHERE for this, and can't find the answer...:

What fuse do I need on the batteries of a SmartUPS 1400 ?

I replaced the batteries on one of mine... (well, tried to!), but the old batteries had leaked a little, and the fuse is fused (!) to one of the battery lugs).

So I need a new fuse to get these batteries swapped out.

Please advise!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • fuse
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
2550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Seller 73volts sells the parts taken from old genuine RBC7 batteries including the anderson connectors, nuts/bolts, terminal caps, and fuses on ebay.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
2550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Hello:

Unfortunately we don't sell the fuse by itself. The reason being is that our RBC cartridges all come with the necessary fuses between the batteries. Use of third party batteries is not something we recommend. I understand if you are trying to save some money by replacing your own batteries. Some have luck doing this, others don't. Results definitely may vary as the UPS is designed to operate with a specific battery. Often times batteries not designed for the UPS will not last nearly as long as others, and in the worst cases could end up swelling or leaking.

With all that said, I'd be glad to leave this thread open for some folks to give you some unofficial advice on this, if anyone has any personal experiences. Just figured I'd first let you know APC's stance on this, and why we do not offer the fuse separately.


Good luck!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
2550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Often times batteries not designed for the UPS will not last nearly as long as others,
and in the worst cases could end up swelling or leaking.
Interestingly enough, the only batteries that have ever swelled up in my APC UPSes have been "genuine" APC ones.

So far as "genuine" APC batteries go, having disassembled quite a few such battery packs over the years, the batteries used have ranged from Panasonic to Best Battery (aka BB Battery, Best and Best Battery) with the Panasonic generally lasting the longest (longevity also depends on UPS usage/power quality/load etc).

Of course, one should always choose the UPS version (aka "standby") of battery which may cost slightly more, but which will last significantly longer in typical UPS usage (long periods of standby punctuated with infrequent deep discharges).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
2550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Looking at the photo's of RBC25 battery packs, I have found the fuse that you require.

It is a 60A LITTELFUSE. Manufacturers part number: 0299060.ZXNV - Automotive Fuse

Any electronics retailer, such as maplin, radio shack should be able to supply this.

Hope this helps

Paul

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
2550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

As a reminder:

APC does not support the use of 3rd party batteries in anyway. They have not been tested in the UPS and the results of using them can not be guaranteed. Using them could result in, but not limited to, the battery leaking acid. If you use a 3rd party battery any and all warranties on the UPS will be void.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

0 Likes
0
2551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:28 PM . Last Modified: ‎2024-03-14 04:28 AM

Seller 73volts sells the parts taken from old genuine RBC7 batteries including the anderson connectors, nuts/bolts, terminal caps, and fuses on ebay.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore