What are the potential causes of "UPS: Bypass not in range ; distorted waveform"?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • What are the potential causes of "UPS: Bypass not in range ; distorted waveform"?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
3
5653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

What are the potential causes of "UPS: Bypass not in range ; distorted waveform"?

Our Smart-UPS SRT 5000's are getting a distorted waveform that is causing email notifications (10+) at the time of the incident. The electricians on staff say that there isn't anything wrong with the power but I'm not convinced. Could someone provide me a bit more information as to what could be causing this?

My apologies if this is posted in the wrong section.

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • apc
  • power
  • srt-5000
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
0
5645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

Please disable the Green Mode in NMC Login> Configuration> Power Setting then Unchecked the Green Mode. If Still Problem persist then Update the Firmware of SRT as they have mentioned in firmware update logs Release Notes (UPS 04.1): ========================= 1. Improved battery charger response time during rapid ambient temperature changes. 2. Updated battery replacement algorithm to handle batteries whose preformance exceeds typical. 3. Improved bypass transfer response time at high overloads

See Answer In Context

  • Tags:
  • SRT5000
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
0
5646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

Hi David, 

Since the SRT5K can handle a large input voltage range, you will most likely see this message when you are inputting a different voltage than what you have the output voltage set to. By default, the output voltage of the UPS is set to 208V, but if you are inputting much higher voltage, most commonly 240V, this message is common. 

You can also see this message when the frequency is out of range, +/- 3Hz. The default frequency is set to 60Hz. 

Can you please provide a copy of the event and data logs for me to look over?

Regards, 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
0
5645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

I've attached the event and data logs for both UPS in that rack, but as a note while going through them we have monthly generator tests which could be why we are getting those distorted wave forms. Also, if you wouldn't mind also taking a look at the events on 10/17/2016, we had a very obscure power event while trying to set the IP of the UPS. Our whole VM rack went down after the UPS were mysteriously commanded to turn off. We really don't want this to happen again as it took some of our systems down for multiple hours.

Thanks,

David

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

0 Likes
0
5646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:05 AM . Last Modified: ‎2024-03-18 11:41 PM

Please disable the Green Mode in NMC Login> Configuration> Power Setting then Unchecked the Green Mode. If Still Problem persist then Update the Firmware of SRT as they have mentioned in firmware update logs Release Notes (UPS 04.1): ========================= 1. Improved battery charger response time during rapid ambient temperature changes. 2. Updated battery replacement algorithm to handle batteries whose preformance exceeds typical. 3. Improved bypass transfer response time at high overloads
  • Tags:
  • SRT5000
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore