I would like to set the default state of each outlet on an AP8930 so that when I power on a PDU certain outlets always are on and others are off.
How can I do this in the administration console?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:05 AM . Last Modified: 2024-03-18 11:41 PM
Hi Robert,
With this PDU, you can configure certain outlets to always be off, unless you turn them back on manually. This is done by going to Configuration -> RPDU -> Switched Outlet -> Configuration. See below:
Then you click on which outlet you would like to configure, and under Switched Outlet Functionality, the default state is Immediate Power On, but you can also choose Never Power On or set a power on delay. See below:
Let me know if that setup will work for you.
Regards,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:05 AM . Last Modified: 2024-03-18 11:40 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:05 AM . Last Modified: 2024-03-18 11:41 PM
Hi Robert,
With this PDU, you can configure certain outlets to always be off, unless you turn them back on manually. This is done by going to Configuration -> RPDU -> Switched Outlet -> Configuration. See below:
Then you click on which outlet you would like to configure, and under Switched Outlet Functionality, the default state is Immediate Power On, but you can also choose Never Power On or set a power on delay. See below:
Let me know if that setup will work for you.
Regards,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:05 AM . Last Modified: 2024-03-18 11:40 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:05 AM . Last Modified: 2024-03-18 11:40 PM
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.