Hi guys
is any one know the meaning of this data point in " ACRC30x modbus register map "
40212 00D3 211 UNIT_MAX_RACK_INLET_TEMP R 2 INT32 (Tenths Deg) F
i mean what is exactly show in this register ?
thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:05 AM . Last Modified: 2024-03-18 11:40 PM
Hello. This point will display the Maximum rack inlet temperature sensor reading that is connected up to the unit. Each unit only comes with 1 sensor, but up to 3 additional rack inlet sensors can be purchased and added to the unit.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:06 AM . Last Modified: 2024-03-18 11:40 PM
Hello. Unfortunately through modbus it will only read the max rack inlet temp. There are no points for the individual rack inlet sensors.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:05 AM . Last Modified: 2024-03-18 11:40 PM
Hello. This point will display the Maximum rack inlet temperature sensor reading that is connected up to the unit. Each unit only comes with 1 sensor, but up to 3 additional rack inlet sensors can be purchased and added to the unit.
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:06 AM . Last Modified: 2024-03-18 11:40 PM
thanks.
so how can read the other 3 sensor temperature on modbus ? i didn't find any address on modbus register map.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:06 AM . Last Modified: 2024-03-18 11:40 PM
Hello. Unfortunately through modbus it will only read the max rack inlet temp. There are no points for the individual rack inlet sensors.
Thank you