Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
We have a different time with e-mail alrms.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: â2025-06-0404:33 AM
Typically the date and time is setup and defined on the local target UPS. The time zone, NTP, and DST if applicable is set.
The NTP should be defined to poll every 8 hours and use an internal NTP Source. If an external source is being used insure you define two different ones and validate they are reachable and not blocked due to the 8 hour polling.
Once the target machine has been properly setup. Initiate a email test and validate it comes through and confirm the date & time are correct.
If your company uses any of the APC Smart Connect Cloud Portal Services. Insure all date and time parameters are also set and defined correctly for your region as outlined above.
Validate by inducing a fault on the target UPS and checking if the email generated is accurate.