Warning - InRow RD: Controller Reset - Cold Start because of a breakpoint.
  • Warning - InRow RD: Controller Reset - Cold Start because of a breakpoint.
5060
142
Posted: ‎2021-06-28 12:03 AM . Last Modified: ‎2024-03-18 11:42 PM
2300
Hi Everyone,
We're just had our inrow unit issue the following alerts:
12.10.2016 06:33:14 InRow RD: Relay output abnormal state no longer exists.
12.10.2016 06:33:12 InRow RD: Compressor drive communication fault no longer exists.
12.10.2016 06:32:58 InRow RD: Relay output abnormal state exists.
12.10.2016 06:32:55 InRow RD: Compressor drive communication fault exists.
12.10.2016 06:32:51 InRow RD: Controller Reset - Cold Start because of a breakpoint.
The unit is online with no pending unit/group level alerts. I haven't been able to track down what "cold start because of a breakpoint" actually means. Is this indicative of an issue? Or is it normal/maintenance and can be ignored?
This is an ACRP:
Model Number:  IR25
Serial Number:  UK1203113006
Controller Firmware:  4.18.0
Hardware Revision:  C8
Date of Manufacture:  01/16/2012
VFD software ver.:  01.07
VFD ID Powercard:  SW:01.02 EE:03.23
VFD serial number:  193215G041
Thanks in advance!
  • acrp
  • alert
  • cooling
  • inrow
Hello. This error means that the programming encountered an error and needed to reboot itself to clear the issue. If this has only happened once, keep an eye on the unit and see if the alarm returns. If not the unit is fine and will continue working. If it does come back please call into your local tech support as they can look deeper into exactly what is causing the issue.
Thank you
Thank you
Thanks very much for your prompt response - that is what I suspected, so it is good to hear it. This unit has been up for well over a year (since last service) absolutely rock solid, so I will continue to monitor it for now. If it recurs, I'll reach out to our local tech support cool
Marcus.