VT units question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • VT units question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 03:31 AM . Last Modified: β€Ž2024-03-19 01:46 AM

0 Likes
4
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 03:31 AM . Last Modified: β€Ž2024-03-19 01:46 AM

VT units question

I've gone through the calculator function, to determine what kind of solution I need. Came out at just under 10k watts, and the three solutions offered were a Symmetra 12k, and 2 VT units. The Symmetra offered showed that we'd be at 99% max capacity, so I ruled that out. The others showed we'd be at 40% capacity. Anyway, I've looked at all the documentation I could find on the VT units, but couldn't figure out what else I'd need, in order to get the power to my servers. There was no mention of how to hook up PDUs, or whatever else I may be using to get the servers powered. Could someone please clear up my confusion for me?

Thanks,

Joe

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

0 Likes
0
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

I've gone through the calculator function, to determine what kind of solution I need. Came out at just under 10k watts, and the three solutions offered were a Symmetra 12k, and 2 VT units. The Symmetra offered showed that we'd be at 99% max capacity, so I ruled that out. The others showed we'd be at 40% capacity. Anyway, I've looked at all the documentation I could find on the VT units, but couldn't figure out what else I'd need, in order to get the power to my servers. There was no mention of how to hook up PDUs, or whatever else I may be using to get the servers powered. Could someone please clear up my confusion for me?

Thanks,

Joe

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

0 Likes
0
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

The calculator recommended the SUVT30KF3B4S, with a 2 battery XR unit. As I mentioned in the original post, we will be sitting around 40% of max capacity of this device. I've since learned that the answer to my original question is that an electrician would be needed to hard wire the receptacles into the back of the unit, so that solves that question. However, I'm starting to wonder if this unit wouldn't be overkill for our server room. I haven't actually spoken with anyone in person yet, I like to do as much footwork ahead of time as possible first. I e-mailed the results of my configuration attempt to myself, and the link shows a total power usage of 9487 Watts, so I'm wondering if maybe a 20K unit would be better utilized, as we really don't have plans for any further expansion, as far as number of servers/devices that would need backup. Any future server purchases would be more for replacement, and not expansion.

Reply

Link copied. Please paste this link to share this article on your social media post.

cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

0 Likes
0
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

Maybe a 40KVA UPS is overkill for your server room. You are really the best judge of that. If you have a 10KW load, the ISX20KF will give you 85% expansion capacity for power, and the ability to add racks and racks of runtime battery. This is a 3-phase UPS with N+1 capability at 20KW

The Symettra LX 16 kva scaleable to 16 kva will also fit the bill, giving you an equivalent level of N+1redundancy, but very little UPS expansion capacity. This is a single phase UPS.

Anything in the capacity range of your server room (10 KW) will require a hard wire input connection by an electrician.

It's time to talk to someone in person πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

0 Likes
0
1245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

My office number is 301.482.1279

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

0 Likes
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-26 03:32 AM . Last Modified: β€Ž2024-03-19 01:46 AM

I've gone through the calculator function, to determine what kind of solution I need. Came out at just under 10k watts, and the three solutions offered were a Symmetra 12k, and 2 VT units. The Symmetra offered showed that we'd be at 99% max capacity, so I ruled that out. The others showed we'd be at 40% capacity. Anyway, I've looked at all the documentation I could find on the VT units, but couldn't figure out what else I'd need, in order to get the power to my servers. There was no mention of how to hook up PDUs, or whatever else I may be using to get the servers powered. Could someone please clear up my confusion for me?

Thanks,

Joe

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore