VMWare no longer supports VMA on ESXi 6.7. PSNS still requires it. Anyone know what solution APC is offering to address this and when it will be available?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:18 AM . Last Modified: 2024-03-08 02:41 AM
Nice. Thanks. I'll look into this ASAP.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:18 AM . Last Modified: 2024-03-08 02:42 AM
Hi,
We offer a CentOS VM that has PowerChute Network Shutdown pre-installed. You would deploy the VM and then login to PowerChute using a web browser to configure PowerChute. Below are links to the install guide, the User's guide, and the download page.
Install guide https://download.schneider-electric.com/files?p_Doc_Ref=SPD_PMAR-9HBK44_EN
User's guide https://download.schneider-electric.com/files?p_Doc_Ref=SPD_PMAR-9DNLQK_EN
Download page https://www.apc.com/shop/us/en/categories/power/uninterruptible-power-supply-ups-/ups-management/pow...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:18 AM . Last Modified: 2024-03-08 02:41 AM
Nice. Thanks. I'll look into this ASAP.