Using two Smart UPS X-3000 and servers with dual power supplies to extend up time

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Using two Smart UPS X-3000 and servers with dual power supplies to extend up time
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
kds86_apc
Crewman kds86_apc
Crewman

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

0 Likes
4
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

Using two Smart UPS X-3000 and servers with dual power supplies to extend up time

I have two Smart UPS X-3000 units and four host servers (3 in a VMware cluster and 1 a Linux server). Each of the servers have dual (redundant powers supplies), and I have one power supply from each server plugged into to one of the X-3000's, and the other power supplies plugged into the second X-3000. It occurred to me the other day that in this scenario we could almost double our up time if we could have one X-3000 carry the servers until reaching a critical battery state, then trigger/transfer to the other X-3000 to carry the servers' other power supplies until either it runs out of battery power or line power is restored.

Is there a way to configure these X-3000s to do this, and if yes, how? 

Thanks for your assistance,

Kevin

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
kds86_apc
Crewman kds86_apc
Crewman

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

0 Likes
0
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

Thanks voidstar for your input as well! 

I will consider the extended run batteries as a way to get more up time. 

Thanks again to both of you!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

0 Likes
0
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

Hi Kevin - 

Unfortunately there is no real way to do this with the Smart-UPS, as they will both switch to battery when they lose input power. The way we work with extended runtime is by supporting external battery packs. By adding external packs you will extend your runtime while maintaining a full redundant solution. 

Reply

Link copied. Please paste this link to share this article on your social media post.

kds86_apc
Crewman kds86_apc
Crewman

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

0 Likes
0
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

Thank you for your reply, Liam!

Do you know of any other APC units of comparable capabilities to these X-3000's that does offer what I described as wanting to do?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

0 Likes
0
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

It's not supported by APC but in theory if your dual supplies are set up so only one is active at a time (ie, it has a preferred source), it'll drain the first UPS and then drain the second one. You'll want to use the second UPS to trigger safe shutdown.

Part of the problem though is that both UPSes will go on battery so they can continue to operate after the power fails. So you won't get double the runtime this way... the second UPS battery will have partially drained before your server switches over to it.

Because of that and additional failure modes, I agree with Liam: extended run batteries would be a safer bet. Your SmartUPS X has a blue connector on the back to accept them.

Reply

Link copied. Please paste this link to share this article on your social media post.

kds86_apc
Crewman kds86_apc
Crewman

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

0 Likes
0
765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:10 AM . Last Modified: ‎2024-03-18 12:46 AM

Thanks voidstar for your input as well! 

I will consider the extended run batteries as a way to get more up time. 

Thanks again to both of you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of