Ups does not shut down my server
Dear All,
I am joined a company as a new network admin and i did discover that the UPS had a problem
its a APC smart 1500VA USB n serial model SUA1500I
the replace battery light was on
so the dealer replaced with new batties and the UPS is fine
i did connect my windows 2003 server with the smart UPS and it detected fine and after installing the software
PowerChute Business Edition v8.0.1 for Windows
i logged into and tried to setup automatic shutdown
by using configure in the protected mode section
but the UPS does not shut down the server
but if i double click on the file shutdown.exe which is in the agent directory the windows 2003 server shuts down gracefully
apprecite if somneone can help me with the settings
i would like 15 minutes for the server to be on batteries after a power failure . if power is not restored after 15 minutes the ups should shut down the server
apprecite your kind reply and help
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:00 AM
Simon,
Thank you very much for letting us know the outcome, I am glad that it suits your needs. Please feel free to post any questions, comments or suggestions that you might have.
JonPro
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:01 AM
Simon,
Have you configured the Low Battery Signal under Protected Systems-->Shutdown settings? If you have not configured, then please set the Low Battery Signal in order for the PCBE to initiate the graceful shutdown when the UPS runtime is remaining X minutes. Please view the attached screen shot for your reference.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:01 AM
Good day Simon,
If you would like to shutdown the server after running on battery for 15 minutes kindly access the web interface of your PowerChute Business Agent by typing in http://127.0.0.1:3052 on the browser were our software is installed. It will ask you to login so please type in the username and password that you have set. Once you are on the Agent interface click on Events and the Actions. Under the Warning section look for the one that says Time On Battery Threshold Exceeded and then click on it. On the configuration page, set it to +15 minutes+ and then down below where it says Initiate Shutdown Sequence please make sure that there is a check mark.
Please see the attached image for your reference.
JonPro
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:01 AM
You can try the Jon's method..it suits your requirement. I didn't think about this option earlier 🙂
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:00 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:00 AM
Thank you guys so much really apprecite your immedite reply.
will check it out tomorrow since today a holiday
regards
simon
really thankful for ur advice n help
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:00 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:00 AM
Dear Jon,
A million thanks for ur advice
woww it worked like a charm
indeed so grateful to u
by the way it does not shut down the server after the specified time but also shuts of the UPS
thats jus so marvelous.
exactly what i wd really want too
once again thnk you so muc and really apprecite
regards
simon
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:14 PM . Last Modified: 2024-03-14 03:00 AM
Simon,
Thank you very much for letting us know the outcome, I am glad that it suits your needs. Please feel free to post any questions, comments or suggestions that you might have.
JonPro